Where we can use 3.5c cables instead of 4c cables.Why?
Answers were Sorted based on User's Feedback
Answer / pakshi rajan.g
only the leakage current flows through neutral in a 3phase system, so size 0.5 core is enough for neutral...
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / sourabh vishwakarma
from 3.5c cable we can save cost instead of using 4c cable.in 3.5c cable .5c is using only for neutral for completing path.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / ajarasheed
it can be used in 3ph equipment connection where the nuetal
will be used only for controls.
Is This Answer Correct ? | 5 Yes | 4 No |
IT DEPENDS ON THE LOAD SITUATION AT THAT PARTICULAR PLACE. IN CASE THERE IS MOE THAN 50% MOTOR LOAD I.E. 3 PHASE LOADS ONLY AND LESS OF SINGLE PHASE LOADS; THEN IN THAT CASE WE COULD USE 3.5C CABLES. BUT WHERE THE AMOUNT OF SINGLE PHASE LOADS ARE MAXIMUM AS COMPARES TO 3 PHASE LOADS; THEN IN THOSE CASES IT WILL BE NECESSARY TO USE 4C CABLES.
Is This Answer Correct ? | 1 Yes | 0 No |
How can you test the vector group of power transformers?
what is Aircraft earthing and what does it do?
what is the function of garing capacitir in SF6 circuit braker?
WHY EXCITATION OF SYNCHRONOUS MACHINE IS DC NOT AC
how i calculate the syncrones generator NGR resistance .if we have a 6mw generator line voltage of generator 11kv also line current 393.3 ampere.
If there is volagte between earth and neutral, what should be the reason ? and solution * What should be allowable limit in case, if the voltage between earth and neutral exist ? / OR what is limit for safe voltage between earth and neutral?
I have 12MW gas engine based power plant its running parallel with grid. my problem is When cpp run in island mode(without geb) that time geb transformer power factor is 0.2 lagging. When cpp run with parallel that time power factor is 0.94 lagging So how can i maintain power factor ofgeb transformer in island mode 0.9 lagging?
what is the difference between control transformer and Potential transformer (PT)?
If a fan get trip and run in reverse direction due to system flow. Now in this condition during starting how can a VFD bring this negative speed to zero and later run in forward direction?