Where we can use 3.5c cables instead of 4c cables.Why?
Answers were Sorted based on User's Feedback
Answer / pakshi rajan.g
only the leakage current flows through neutral in a 3phase system, so size 0.5 core is enough for neutral...
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / sourabh vishwakarma
from 3.5c cable we can save cost instead of using 4c cable.in 3.5c cable .5c is using only for neutral for completing path.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / ajarasheed
it can be used in 3ph equipment connection where the nuetal
will be used only for controls.
| Is This Answer Correct ? | 5 Yes | 4 No |
IT DEPENDS ON THE LOAD SITUATION AT THAT PARTICULAR PLACE. IN CASE THERE IS MOE THAN 50% MOTOR LOAD I.E. 3 PHASE LOADS ONLY AND LESS OF SINGLE PHASE LOADS; THEN IN THAT CASE WE COULD USE 3.5C CABLES. BUT WHERE THE AMOUNT OF SINGLE PHASE LOADS ARE MAXIMUM AS COMPARES TO 3 PHASE LOADS; THEN IN THOSE CASES IT WILL BE NECESSARY TO USE 4C CABLES.
| Is This Answer Correct ? | 1 Yes | 0 No |
what is errection pcbs?
How to measure power in 2 or 4 or n phase circuit? Please give me a formula.
What is meant by soft starter used in motors?
What current flows in the transformer primary when its secondary is open?
what is difference between 2 pole structure and 4 pole structure in transformer yard
WHY DOES NEUTRAL DO NOT CARRY EVEN THOUGH IT CARRIES RETURN CURRENT?
State the types of distortions in amplifier?
Two electric lamps 40 W, 220 V each are connected in series across 220 V. What is the power consumed by the connection?
2 Diesel Generators 900KVA connected to the bus bar for essential load as an alternative for power taken from 11/440V 3KVA Transformer supplying this bus bar. my question here is in the event of power failure on 11KV side can I feed the power to 11 KV bus by using the same transformer as reverse feed, what will be the inrush current???
High voltage test procedure of in swgr board. why should measure millivolt drop on testing time?
briefly explain the main blocks found in a microprocessor based system
Does dry and oil transformers both require dedicated neutral, because in my project we are using 2500kv dry star delta transformer, where they say neutral not required and even it is not provided in our substation. can u let me know
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)