OUR METER READER TAKE READING OF INDUSTRIAL CONSUMER.THEY
ALWAYS ASK HOW TO INCREASE POWER FACTOR FROM 60% TO 99 % TO
AVOID PENALTY OF POWER FACTOR.
Answers were Sorted based on User's Feedback
Answer / zahid noor
Power Factor can be improved by installing Capacitors at
the end of consumer, why it is required, in order to
fulfill the loss during transmission of power to the end
of consumer, henceforth if consumer installs additional
capacitors for making this loss, penalty for PF below .95
can be avoided & for PF above .95 to unity , extra rebate
on monthly bills can be availed. Henceforth It is always
beneficial to achieve PF up to Unity.
In order to calculate the KVAR of capacitors to be
installed, it is required to know the details of consumer
regarding load, voltage level, type of load, switching
operations of load so as to finalize the capacity required
for achieving the same.
Is This Answer Correct ? | 5 Yes | 1 No |
The power factor is low for industrial customer because the load is usually inductive due to the many motors installed.
Power supply companies sell by calculating KWH used.Thier generators maximum capacity is limited by the amps the generator can produce at a fixed voltage.
So calculations will tell u that lower power factor means higher amps for the same KWH &AND HIGHER PF MEANS LOWER AMPS for the same kwh. thus the power supply companies can make more money from the same generator and also save on other expenses.
power factor is improved by connecting reactive load in parallel.this reactive power is loss free and you dont pay for the power consumption.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / t.mohan
POWER FACTOR = REAL POWER / REACTIVE POWER.KWH/KVRH.
FOR INCREASING POWER FACTOR PROVIDE CAPACITOR BANK AT
CONSUMER'S END.
Is This Answer Correct ? | 1 Yes | 0 No |
1000 W bulb takes 4.16 Amps at 240 volt then what will be the KWH & if i am using 1000 W bulb at 180 Volt the amps will be 5.55 then what will be KWH????????????????
Why it need to form a capcitor when it not been in use from three or two year. Plz describe it technically.
how can calculated the rating of the 11 KV transformer?
how we calculate capacitor bank mvar for 11 kv distribution networ , and i need releation between capacitor bank with voltage, frequency, current, pf
difference between servo motor and synchronous motor
Can i use to 3 phase 4 wire energy meter inplace of 3 phase 3 wire energy meter ?
whu does the power factor of diesel generator always be 0.8. please explain
what do you mean by every IC 74 first digit.why are you using this no.why not using another no.
What is ST and specify its range of voltage.
I am getting above 60 V as open delta voltage against single phase unit ICT at tertiary delta formed and ICT getting trippped on NDR. ICT tested and found in order. PTs provided on tertiary are tested and in order. what may be the reason?
How to measure the Harmonic Distortion of UPS ie THD?
what is the min and max ohmic resistance for the earthing rod installed for lighting poles for street light network