OUR METER READER TAKE READING OF INDUSTRIAL CONSUMER.THEY
ALWAYS ASK HOW TO INCREASE POWER FACTOR FROM 60% TO 99 % TO
AVOID PENALTY OF POWER FACTOR.
Answers were Sorted based on User's Feedback
Answer / zahid noor
Power Factor can be improved by installing Capacitors at
the end of consumer, why it is required, in order to
fulfill the loss during transmission of power to the end
of consumer, henceforth if consumer installs additional
capacitors for making this loss, penalty for PF below .95
can be avoided & for PF above .95 to unity , extra rebate
on monthly bills can be availed. Henceforth It is always
beneficial to achieve PF up to Unity.
In order to calculate the KVAR of capacitors to be
installed, it is required to know the details of consumer
regarding load, voltage level, type of load, switching
operations of load so as to finalize the capacity required
for achieving the same.
| Is This Answer Correct ? | 5 Yes | 1 No |
The power factor is low for industrial customer because the load is usually inductive due to the many motors installed.
Power supply companies sell by calculating KWH used.Thier generators maximum capacity is limited by the amps the generator can produce at a fixed voltage.
So calculations will tell u that lower power factor means higher amps for the same KWH &AND HIGHER PF MEANS LOWER AMPS for the same kwh. thus the power supply companies can make more money from the same generator and also save on other expenses.
power factor is improved by connecting reactive load in parallel.this reactive power is loss free and you dont pay for the power consumption.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / t.mohan
POWER FACTOR = REAL POWER / REACTIVE POWER.KWH/KVRH.
FOR INCREASING POWER FACTOR PROVIDE CAPACITOR BANK AT
CONSUMER'S END.
| Is This Answer Correct ? | 1 Yes | 0 No |
why neutral busbar size is SAME of the phase busbar size UPTO 200A IN LT PANELS
Can I Drain A Oil For Sample When The Transformer is Running? (Charged)
cab we add capacitor bank with generator to improve power factor or not??????
which technique servo motor tested o.k or faulty ?
How to design a Unit auxiliary transformer for a power house having a unit of 65 MW and Generating voltage of 11 KV and Secondary voltage of 433V
what is 33 /11kv transformer bdv
Suppose a 3 phase, 2 pole, 440V induction motor is driving a flywheel of 600mm diameter, 150kg mass. By using v-belt and pulley, the speed is increased to 4500 RPM. What will be the effect on motor current?
what is the difference between torque induced and torque load?compare them with respect to dc motor?
what is the meaning of Air condition "TON"
diagram for soft stater ?
How to decide DO set rating of Transformer?
why battery room in substation is black coloured?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)