I HAVE CONSUMER WHOSE POWER FACTOR IS 65% I WANT TO INCREASE
IT TO 98%.HOW TO CARRY OUT?
Answers were Sorted based on User's Feedback
Answer / mubashar ali
you can calculate VRAr, those required for improvment 0.65
to 0.98
KW(Tan1-Tan2)
KW= your total load
Tan1= cos invers of first pf ,than take tan1
Tan2= cos invers of second pf, than take tan2
then u find total KVAr reqird , and installed same rating
capictor
Is This Answer Correct ? | 12 Yes | 0 No |
Answer / mrt
by adding capacitors parallel to the load we can increase
the power factor.Now a days APFC will regualtes the power
factor
Is This Answer Correct ? | 10 Yes | 0 No |
Answer / hm
Power factor improving devices:
1. capacitor banks
2. synchronous condensers
3. phase advancers etc.
synchronous condensers are used in industries but for low
power customers capacitor banks are useful. but only
disadvantage is that if supply voltage does not remain
constant, reactive power generation by capacitor varies so
power factor cant remain at 98%, it fluctuates.
so don't install rated capacitor banks directly,add a
voltage regulator circuit to maintain constant voltage or
better to use APFC.
Is This Answer Correct ? | 6 Yes | 1 No |
Answer / navin
reqd KVAR = KW ( Tan (cos-1 P1) - Tan ( cos-1 P2) )
KW- Load KW
P1- Existing PF angle
P2- Desired PF angle
Is This Answer Correct ? | 5 Yes | 1 No |
Answer / zahid noor
Now a days Automatic Power Factor Control Panels can be
easily purchased from Panel manufacturer by providing them
the details of load, voltage level, current etc & existing
PF , can contact m/s Universal cables Satna, M/s L&T
Switchgear, and some local manufacturers can also supply as
per requirement.
Is This Answer Correct ? | 4 Yes | 4 No |
PROVIDE YOUR LOAD IS VERY USEFUL FOR FINDING OUT
Is This Answer Correct ? | 4 Yes | 6 No |
Answer / rahul
to increase the power factor from 65% to 98%, the consumer
may install certain equipments such as INDUCTION MOTOR etc
which works at leading power factor and hence draws the
lagging reactive component and hence increases the overall
power factor!!!!!!!
Is This Answer Correct ? | 2 Yes | 10 No |
what is the speed of a turbine in an hydroelectric power station and how many poles does it have...?
Pl. give me checklist for installation & commissioning of machine tool.
diff between synchronous gen and alternators
how can calculate 1kva generator running time in 1 liter keroscene
Do you know how to joint the H.T and L.T Cables?
23 Answers KESC, MGVCL, Nokia, Oil Country Tubular, Power Control, SAGT, Siemens, Simco, Vivek Engineers,
please send me jindal previous aptitude and technical question and answer.my email id is deep_raj@live.com
What are the causes for the failures of sandwich type (Al) busducts?
Whot is the braking capacity for MCCB. How we select different braking capacity.
defult setting in p220 micom motor proction relay for 11kv,640kw,f.l.a.-40a,1440rpm ht motor?
what is different between kvar & micro farad when its comes across the capacitor rating is it possible to convert kvar to mf or mf to kvar
How to connect frequency meter in metering circuit?(single phase and three phase frequency meter)
difference between semiconductor & conductor & insulator?