I HAVE CONSUMER WHOSE POWER FACTOR IS 65% I WANT TO INCREASE
IT TO 98%.HOW TO CARRY OUT?
Answers were Sorted based on User's Feedback
Answer / mubashar ali
you can calculate VRAr, those required for improvment 0.65
to 0.98
KW(Tan1-Tan2)
KW= your total load
Tan1= cos invers of first pf ,than take tan1
Tan2= cos invers of second pf, than take tan2
then u find total KVAr reqird , and installed same rating
capictor
| Is This Answer Correct ? | 12 Yes | 0 No |
Answer / mrt
by adding capacitors parallel to the load we can increase
the power factor.Now a days APFC will regualtes the power
factor
| Is This Answer Correct ? | 10 Yes | 0 No |
Answer / hm
Power factor improving devices:
1. capacitor banks
2. synchronous condensers
3. phase advancers etc.
synchronous condensers are used in industries but for low
power customers capacitor banks are useful. but only
disadvantage is that if supply voltage does not remain
constant, reactive power generation by capacitor varies so
power factor cant remain at 98%, it fluctuates.
so don't install rated capacitor banks directly,add a
voltage regulator circuit to maintain constant voltage or
better to use APFC.
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / navin
reqd KVAR = KW ( Tan (cos-1 P1) - Tan ( cos-1 P2) )
KW- Load KW
P1- Existing PF angle
P2- Desired PF angle
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / zahid noor
Now a days Automatic Power Factor Control Panels can be
easily purchased from Panel manufacturer by providing them
the details of load, voltage level, current etc & existing
PF , can contact m/s Universal cables Satna, M/s L&T
Switchgear, and some local manufacturers can also supply as
per requirement.
| Is This Answer Correct ? | 4 Yes | 4 No |
PROVIDE YOUR LOAD IS VERY USEFUL FOR FINDING OUT
| Is This Answer Correct ? | 4 Yes | 6 No |
Answer / rahul
to increase the power factor from 65% to 98%, the consumer
may install certain equipments such as INDUCTION MOTOR etc
which works at leading power factor and hence draws the
lagging reactive component and hence increases the overall
power factor!!!!!!!
| Is This Answer Correct ? | 2 Yes | 10 No |
what is diffential relay? testing proceure?and transformer reach Over load thet time differencilal relay operate or not ?
if the synchronizing b/w generator and busbar not complete and we close the out going circuit breaker of generator then what happen ?
what is the practical application of full adder circuit?
0 Answers College School Exams Tests,
Please explain me abt PQ diagaram in the power sector.
1 sq mm conductor=? how many amps
which type of motor is suitable for water suction pump ?
Please explain, how to test vector group of tranformer(Delta y1) . Thank
Why does increasing the magnetic flux in the main field of a d.c motor cause the armature current to reduce??
why do we use star-delta starter. what is its need?
what are the differant std sizes of cable trenches?
what will happen at secondary side of transformer if i increase voltage at primary side?while V1*I1=V2*I2 will secondary voltage or current increase?
in three phase 11kv transformer (11kv/433v) input( R,Y,B) output (X,Y,Z,N) the connection as follows 1 phase R -open 2phase y connected to both R and y of input] 3phase B- B what is the output voltage X to N ,Y to N , Z to N
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)