I HAVE CONSUMER WHOSE POWER FACTOR IS 65% I WANT TO INCREASE
IT TO 98%.HOW TO CARRY OUT?
Answers were Sorted based on User's Feedback
Answer / mubashar ali
you can calculate VRAr, those required for improvment 0.65
to 0.98
KW(Tan1-Tan2)
KW= your total load
Tan1= cos invers of first pf ,than take tan1
Tan2= cos invers of second pf, than take tan2
then u find total KVAr reqird , and installed same rating
capictor
| Is This Answer Correct ? | 12 Yes | 0 No |
Answer / mrt
by adding capacitors parallel to the load we can increase
the power factor.Now a days APFC will regualtes the power
factor
| Is This Answer Correct ? | 10 Yes | 0 No |
Answer / hm
Power factor improving devices:
1. capacitor banks
2. synchronous condensers
3. phase advancers etc.
synchronous condensers are used in industries but for low
power customers capacitor banks are useful. but only
disadvantage is that if supply voltage does not remain
constant, reactive power generation by capacitor varies so
power factor cant remain at 98%, it fluctuates.
so don't install rated capacitor banks directly,add a
voltage regulator circuit to maintain constant voltage or
better to use APFC.
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / navin
reqd KVAR = KW ( Tan (cos-1 P1) - Tan ( cos-1 P2) )
KW- Load KW
P1- Existing PF angle
P2- Desired PF angle
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / zahid noor
Now a days Automatic Power Factor Control Panels can be
easily purchased from Panel manufacturer by providing them
the details of load, voltage level, current etc & existing
PF , can contact m/s Universal cables Satna, M/s L&T
Switchgear, and some local manufacturers can also supply as
per requirement.
| Is This Answer Correct ? | 4 Yes | 4 No |
PROVIDE YOUR LOAD IS VERY USEFUL FOR FINDING OUT
| Is This Answer Correct ? | 4 Yes | 6 No |
Answer / rahul
to increase the power factor from 65% to 98%, the consumer
may install certain equipments such as INDUCTION MOTOR etc
which works at leading power factor and hence draws the
lagging reactive component and hence increases the overall
power factor!!!!!!!
| Is This Answer Correct ? | 2 Yes | 10 No |
the winding of Generator and Motor is star or in delta ? and why
Is it possible to import & export power through the same power transformer? what will be the vector group normally for both different or same?
why nutral and earthing wire connect with each other in main panel board.?
what percent do you derate your copper wire when you change from copper buss to copper wire
what is meant by servo motor ? how its operating either AC or DC?
Wat is the best to use in a generator a 6.5kva or a 7 kw
Can i use to 3 phase 4 wire energy meter inplace of 3 phase 3 wire energy meter ?
friends., why celling fan rotate cockwise direction and wall fan anticickwise direction ?
If a rotary UPS is in line through grid power; What would be the impact on Power Factor if the load through rotary ups is 25% , 50% , 75% & 100%. Will the power factor reduce with less load?
what is the function of a commutator in a dc generator?
14 Answers College School Exams Tests, NTPC, TCS,
Please explain, how to test vector group of tranformer(Delta y1) . Thank
How to calculate the multiplying factor for energy meter with ct ratio given
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)