how bucchos relay works in a transformer
Answers were Sorted based on User's Feedback
It is a gas actuated relay.It has two floats.
one is top float(bucholz alarm) which is operated when
oil level in transformer decreases and for a minor fault
which is developing.The gas is collected at the top of
bucholz relay, thus displacing the oil in the top and thus
causes the float to fall down and make the NO contact.
The other is bottom float(bucholz trip) which is
operated for a severe fault which causes oil inrush towards
the bottom of bucholz relay and thus causes the float to
make the NO contact thus isolating the supply to the
transformer.Sometimes buchols relay will operate for a
feeder through fault which causes jerk in the transformer
causing oil inrush.
cheers
gova
Is This Answer Correct ? | 17 Yes | 1 No |
Answer / minal
When there is a fault in a transformer gas bubbles are
formed in an oil filled transformer, the bucholz relay
operates & it gets trip .Thus it protects the tranformer
from any fault.
Is This Answer Correct ? | 16 Yes | 4 No |
Answer / gajanan
The Buchholz relay is installed at the middle of the
connection pipe between the Transformer tank and the
conservator.
for the fault in transformer it actuates the alarm or the
Transformer is disconnected from the circuit for severe
fault
Is This Answer Correct ? | 14 Yes | 4 No |
Answer / vinayak khorate
In oil filled transformer the bucchos relay is mounted in
between connection pipe of Transformer tank and the
conservator.
When fault occurred(slow occurring faults) the oil near by
winding gets heated and decomposed due to which gas bubbles
are release. This bubbles get stuck in the Oil chamber of
reply and hence send the tripping signal. When the fault is
heavy large number of gas bubbles are released, when they
pass over the bucchos reply the tripping mechanism in between
gets triggered and Transformer is disconnected from the
circuit for severe
fault
Is This Answer Correct ? | 6 Yes | 0 No |
Answer / gunasekaran
during the incifient fault 75%H2 gas will be form in the
transformer is gas accumulate at buchholz relay first it
will give alarm then trip
Is This Answer Correct ? | 2 Yes | 2 No |
Answer / anil kumar
whenever it is incipient fault in transformer, the gaseous formation take place which moves up wards from bucz relay, and replaced the oil in upper tub and press the tub , so due to mercury switch, ckt will complete & alarm will appear , if further severe fault , the oil pr. increases in tank and will go in conseverator tank through buz relay which makes press the bottom tub forcibly and trip the ckt .
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / mukesh vaghela
Buchholze relay is gas operating relay when internal fault occurs transformer in transformer like wdg installation damage then oil heat above level and boobles done and go up and its pressure operate buchholz relay. It is only relay which operate before fault occurs in system.
Is This Answer Correct ? | 0 Yes | 0 No |
how is working the APFC when varying the load?
How to calculate phase to phase difference ?
why the Different manufacture's rating of Gas genset are different? i.e : cummins genset rating is in KVA .( 625kv). While GE- Jenbacher make genset have rating in Kw. (625 kw)
which loses are in transformer .explane each loses
why fault current time duration is calculated for 1 minutes?
1 Answers Rockfort Engineering,
I find that underground strip-armoiured,4core,LT PVC cables in an earthed power distribution sytem are occasionly found in charred condition-with no trace of it except ash. Is this because of no proper earth connection/continuity (giving rising to high armour resistance)in the joint enroute or because of insufficient capability (again due to high armour resistance)of cable-armour to carry fault current or due to neglected /unprotected overloading of the cable or due to high armour currents caused by power thefts where only phase(s) are unauthorisely tapped & at the point of poer consumption earth terminal is established by burring underground a not so good earthing rod (or using an underground water pipe for the purpose)
We use ACB in LT and VCB in HT.But if we use VCB in LT and ACB in HT that what will be the effect on the system or any power range?
my self i am raghu working as tech.. in my college the maximum demand is 211 kva presently we are using 12kva capacitors the target power factor is .95 so what capacity of capacitor banks should i install
some basic standard questions on transformer.
what is formula to cal cute earth pit numbers and size of earth strip used in earthing?
IF ANYONE HAVE ANY QUESTION ASK ME AT MY MAIL anmol.bhardwaj5@gmail.com
what effect on electrical equipment if PF is gone over 0.996 in leading when provider say that its keep in minimum 0.996lagging