What will happen if " not connecting the neutral point to
ground of diesel generator output (380 V)", also if someone
touched one phase without isolation from ground during the
A/M condition what will happen to him?
Answers were Sorted based on User's Feedback
Answer / vedprakash uppadhaya
basically the neutral terminal provide return path for the
conduction .if we dont used neutral then no return path
will appear .and in that case if we touche the neutral then
we will be shocked.also neutral terminal is used for phase
ballance.
Is This Answer Correct ? | 3 Yes | 3 No |
Answer / arsenal
we wll get shock because the current flows through our body
towards the ground which forms a closed circuit.
Is This Answer Correct ? | 1 Yes | 1 No |
Answer / dhinesh
Due to the potential difference between the generator and earth the person will get shock.As the neutral is not grounded we don't have any option for protection.so the person who touch the phase is under risk of shock.
Is This Answer Correct ? | 0 Yes | 0 No |
what will happen ac motor give to dc supply
9 Answers Areva, College School Exams Tests,
why a single phase induction motor has poor power factor
what happens if dc supply is given to the transformer?
Why the arms of delta in a delta-wye power transmission system are kept constant??
Can anybody tell me the Electrical IS rules website?
Write masons gain formula.
what is phase voltage and phase current what is line current and line phase
if 3400kw slipring motor rotor shorting done and motor started on mv drive ,what will be the rotor shoring current
Why only 1ph,2ph,3ph supplies are universally used?? Why not 4ph or 5ph??
by what factor the starting current is used when comparing star and delta connection for motor starting?
EXPLAIN WHY THE SURGE CURRENT RATING OF AN MCCB OR CIRCUIT BREAKER DECREASES WITH INCREASE IN THE RATING OF MCCB OR CIRCUIT BREAKER.
Magnetizing current for induction motor compared to transformer is= A equal B more C less D depends on load