Answer / atul
Percentage Transformer Impedence is the Voltage drop on the
full load due to the winding resistance and leakage
reactance express as a percentage of rated voltage.
percentage Impedence = Impedence voltage/Rated voltage
*100
| Is This Answer Correct ? | 32 Yes | 12 No |
Answer / giri
Transformer percentage impedence is the percentage of
primary voltage rating of the transformer required to drive
secondary rated current when secondary is shorted.
| Is This Answer Correct ? | 26 Yes | 12 No |
Answer / sujata wagh
Transformer impedence is the voltage drop on full load due
to winding resistance and it express as % impedence.
% impedence is measured during short circuit test.
forluma to calculate % impedence is =
% impedence = impedence voltage*100/rated voltage
where impedence voltage is the voltage applying at one end
for full load corrent, while the other shorted is shorted.
| Is This Answer Correct ? | 12 Yes | 2 No |
Answer / sabareesh kumar.b
Tell the correct answer for IMPEDANCE..............
| Is This Answer Correct ? | 5 Yes | 3 No |
Answer / hussaini dangambo
The percentage impedance of a transformer is the volt
drop on full load due to the winding resistance and leakage
reactance expressed as a percentage of the rated voltage.
It is also the percentage of the normal terminal voltage
that can be applied to circulate full-load current under
short circuit conditions.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / piyush rana
% Impedance is the primary voltage at which the rated
current flows from short circuited secondary winding.
| Is This Answer Correct ? | 0 Yes | 0 No |
How servo stabilizer works.
What is difference between start imitation and start interlock for 3 phase motor protection ?
Dear sir,how should i set the relay in star delta starter..say ex i am having 4ohp motor,,wht should be the relay setting...?
I want to know if it is possible to use Variable Frequency Drive to reduce the current required for starting a motor?
why Transformer and DG rating capacity is in KVA
In Air circuit breaker LSIG protection unit is used. Without fault in cables (2 runs 3Cx150Sq.mm Copper, 1Kv grade, XPLE armored cable IR value is more than 550Mohm @ 500V Megger) and load section Long time Overcurrent protection is triggers and trips the unit. We changed LSIG protection with new factory tested unit. Even then fault is persisting. Please suggest the possible causes
Why the earth to phase voltage is high 250 compare to other two phases
what is the difference between the electrical and electroncis
help me with the question that might be ask on the interview for technical position
Hi frnds :) plz tell me that i have 100 KVA 3 phase generator so by thumb rule 100*1.4 = 144 amps and generaly we can operate at 80% load...so it will 144*0.8 =112 amps.... so now i m confused about single phase load.....if we use that generator only for single phase the that 112 amps is total single phase load or i can give 112 amps at red 112 amps at yellow and 112 amps at blue.... i mean that total single phase load that 100 KVA generator will take is 112+112+112=336 amp ??
give single line diagram of D.O.L and star -Delta starter ?
8 Answers ABS, Al-Shuaah, Alkali Metals, Cabin Crew, Cognizant, CRI, Gwalior Distilleries, Hotels, Logicon Engineers, Max India, Nicomet, Radisson Blu, RK Company, Siemens, SLCM, Solar, Steel Strips Wheels, Sugar Factory, TATA, TCS,
1. what is exciting winding, rotor winding, startor winding. and how it works? in ac generator
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)