Answer / atul
Percentage Transformer Impedence is the Voltage drop on the
full load due to the winding resistance and leakage
reactance express as a percentage of rated voltage.
percentage Impedence = Impedence voltage/Rated voltage
*100
| Is This Answer Correct ? | 32 Yes | 12 No |
Answer / giri
Transformer percentage impedence is the percentage of
primary voltage rating of the transformer required to drive
secondary rated current when secondary is shorted.
| Is This Answer Correct ? | 26 Yes | 12 No |
Answer / sujata wagh
Transformer impedence is the voltage drop on full load due
to winding resistance and it express as % impedence.
% impedence is measured during short circuit test.
forluma to calculate % impedence is =
% impedence = impedence voltage*100/rated voltage
where impedence voltage is the voltage applying at one end
for full load corrent, while the other shorted is shorted.
| Is This Answer Correct ? | 12 Yes | 2 No |
Answer / sabareesh kumar.b
Tell the correct answer for IMPEDANCE..............
| Is This Answer Correct ? | 5 Yes | 3 No |
Answer / hussaini dangambo
The percentage impedance of a transformer is the volt
drop on full load due to the winding resistance and leakage
reactance expressed as a percentage of the rated voltage.
It is also the percentage of the normal terminal voltage
that can be applied to circulate full-load current under
short circuit conditions.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / piyush rana
% Impedance is the primary voltage at which the rated
current flows from short circuited secondary winding.
| Is This Answer Correct ? | 0 Yes | 0 No |
What will be the resultant out put voltage when two different voltage rating batteries are vconnected in parallel? pls. answer with example if available.
definition of transponder?
Hi to u all : Friends: Why when operate on 2 phase welding machine the power metr goes reverse ?? the meter is god on other loads. thanks
Dear sir/mam Iwant complete details of Naintenence of 33kv/433v Transformer having 1250 KVa
WHTA IS LIMT OF LEAKGE CURRENT OF 11 KV 1 CORE 1000SQ.MM. XLPE CABLE.LOAD ON CABLE IS AROUND 600AMP .LENGTH 500 MTRS.
what is the difference between MCCB and SFU in terms of their application?
2 Answers Secure Meters, Tata Teleservices,
IN A HT CABLES i.e. 1.9/3/3 kv, what is the meaning of 1.9 and 3.3.
while selecting transformers for 33 kva feeder normally we ask for 33/433 kv why not 33/415
What are the insulation standerds for eg H clase and how many insulation standerds are there and its standerds??????
what are the differant std sizes of cable trenches?
why the electrolyte level in lead acid battery is maintained 2.5 cms above electrodes?
when we switch on the switch and load is not connected at home,is electricity wasted?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)