What Is Transformer Impedance ?

Answer Posted / hussaini dangambo

The percentage impedance of a transformer is the volt
drop on full load due to the winding resistance and leakage
reactance expressed as a percentage of the rated voltage.
It is also the percentage of the normal terminal voltage
that can be applied to circulate full-load current under
short circuit conditions.

Is This Answer Correct ?    2 Yes 0 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

What is vaccum currcuit breaker.define with cause and where be use it device?

636


What do you mean by ratio correction factor of instrument transformer?

714


What is meant by stator? What is meant by rotor?

642


what is the difference between electrical and electronic choke?

1482


what is the easiest method of short circuit current calculation ? pls. derive with a mathematical example in real life application.

1981






Z transform is use when system is not a) converges b) diverges

1188


how to differentiate a mpcb,mcb with a contactor? Explain their working operation

1660


What is diversity factor in electric installations?

722


in star-delta tranformer,if the input of star connection is 400/7v 3 kva then what is the output of delta connection?

1722


state basic meaning of 'INDUSTIAL AUTOMATION'?

1383


Application Comparison between 22KV (UE)and 33KV (E) system. Are we allowed to use 33KV (E) cable in lieu of 22KV (UE) cable. What are the technical disadvantages.

1853


i have 90kw motor.so i choose connect cable .please what is parameter checked so please give to formula

1736


In case of generator when we consume more power produces by it why load on generator increase and starts sound more. and how it is adjusted..

1444


what is the effect of power factor of machines in starting current

1532


Name a govt approved university which have 100% online engineering course.

1279