what happen when dc shunt motor field is sudden open in
running condition
Answers were Sorted based on User's Feedback
Answer / manish kumar
For a dc shunt motor if field is suddenly opened, no
current flow so no flux and no magnetic field..so according
to MOTOT PRINCIPLE...conductor experiences torque only if
it is placed in magnetic field...hence the speed of motor
decreases slowly due to inertia and finally it stops.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / soumyabrata banerjee
actually in case of dc shunt motor whenever the shunt field coil is open then total flux thats mainly created by the shunt fild winding is become zero then speed become dangareously high so the machine is burn out during the running condition.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / ghanshyam
Is field is open.. Then whole current is flow in armature winding and we knoe that flux of dc shund moter become zero . Due to high current armature produce high speed so moter stare running in high speed condition but moter winding made for a particular current rating..... If we give a high current in armature then temp. Of winding increase and there is a possibility to insulation break down and armature winding may burn.....👍
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / tapeshwar pandey
If shunt field opens the residual magnetism direction will
reverse due to domination of armature reaction and motor
will move in reverse direction.
Is This Answer Correct ? | 0 Yes | 2 No |
Answer / n.ravi teja
when dc shunt motor operates at normal conditions the speed
is constant.and when ever a suddenly field is open, the
field winding is having inductive property so it does not
allow sudden changes in current.open ckt means current
zero.and the rotor(armature) is continue its running
condition because it is connected to generator rotor
shaft.but we know when a current carrying cunductor is
placed in a rotating magnetic field ,it cuts the magnetic
field and emf is induced.but when field is open no current
carrying current is there in that ckt.so no emf is
induced.we know emf is proportional to speed.so speed
decreases .
Is This Answer Correct ? | 2 Yes | 5 No |
Answer / raja
when the motor is under running condition suddenly the
field is open the motor will not stop.
because field is open means the field current is zero but
shunt motors are self excited motors so due to resudual
magnetism the speed of the motor will be decrease.
Is This Answer Correct ? | 4 Yes | 19 No |
when generator short circuit condition, the current how dissipates. or at short circuit voltage not available then current how can flow?
how many units (kwh) are there if in one MW?
Transformer Parallel Operations
List few applications of d.c series motor?
A group of machines (wind turbines) connected with 33KV feeder and each machines are having individual VCB. The 33KV feeder connected with 110KV/33KV substation. The 33KV feeder tripped by over current at Substation and fault recorded at Substation as OC-R&Y phase. Same time the group of machines VCB tripped by over voltage, the fault recorded voltage was above 66KV by numerical Under/Over voltage relay. While grid drop time, this much of voltage hike is possible?
What is the main cause of magnetism?
in power station what is the electrical circuit length of spacing between power transformer and lightning arrestors,for the voltage system of 230kv,110kv,33kv,22kv,11kv?
if name plate detals of a motor or any other is missing then how to find it
what's prime importance of protection in electrical system.if protection system don't work properly what can happen in electrical system?
What is oil temprature with A/T contacts in Transformer ?
Which type starter is used for synchronous motor?
What should be the BDV value of a new transformer oil