11kv alternator commissioning test?
Answers were Sorted based on User's Feedback
Answer / naveen singh
Before commissioning of alternator following electrical tests should be done on site-
(1) IR and PI of generator
(2) Winding resistance of generator
(3) IR and winding resistance for PMG and excitor field winding.
| Is This Answer Correct ? | 19 Yes | 1 No |
Answer / noel
You should check that the alternator is aligned properly
with the generator motor. this should be done according to
the manufacturers specs. Rotate the alternator and check the
gap between the rotor and the stator. Also this should be
provided by the Manufacturer. Then take and IR and PI test
and record your findings. Check that the data is on the
right parameters. And also check the wirings for the CTs.
Depending if they are European or US manufactured the flow
of the current may vary a give you incorrect trips during
commissioning.
| Is This Answer Correct ? | 6 Yes | 1 No |
what is dc transformer? how it work?
I am EEE student i want to improve my core side skills.how cn i approach it?
How to calculated capacitor rating both HT
how to calculate the size of cable for 100 kva load,?can somebody tell me with a formula
3 pahase 750kva Running 2 DG sets in 35 mints.525ampers. and 616 kw how much fuel consumption in Generator.what is the formula.
1 Answers Delite Systems Engineering,
Following test should be conducted to find out relative polarity of transformenr terminals A no load test B back to back test C phasing out test D none of above
how do we select a copper power cable for a 10 HP, 1440 rpm, 440V, 3 phase AC motor?
Why in India distribution transformer are connected in Dyn11 when we know capacity of v-v connection can be increased by adding only a single transformer?
What is an Automatic Voltage Regultor & what is its use? What are the general componets we use to design an Automatic Voltage Regulator..What are the factors to be considered for its design?
1. What is maximum permissible distance between smoke detectors ? 2. How do we decide number of smoke detectors required in a large office, warehouse, hall etc ? 3. What should be maximum height of smoke detectors ? 4. Where do we use heat detector, optical smoke detector, temperature sensitive detector ?
Difference between ups and invertor
how many types of accuracy class in ct? what is meaning of 5p20?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)