what is the effect if we add capacitor on DG supply, it has
any loss or benefit.
Answers were Sorted based on User's Feedback
Answer / a.kannan
The above answer is correct And what I have experienced is
whenever we put the fixed capacitor in parallel to DG , at
any moment if load falls to certain value then consequence
KVAr (inductive ) will also reduce.Due to the fixed
capacitor the available KVAr(capacitance)is excess in the
circuit.This leads to leading current in the generator
armature circuit.Armature reaction takes place with this
leading currrent that causes excess induced EMF that
results in high voltage.this high voltage reference may be
harmful to AVR of the alternator.
| Is This Answer Correct ? | 20 Yes | 0 No |
Answer / arun
Alternators are normally designed at 0.8 pf lag.It is not
advisable to run DG with capacitor banks switched ON.But as
you approach to maximum loading the winding temp.may
increase leading to tripping if cooling of alternator is
not efficient.In such a case you can put ON a few capacitor
banks & monitor the pf.Maintain pf somewhere between 0.85
to 0.90 lag.Result is the current drops and so is the
alternator temperature.This we have practically done with
our DGs.
| Is This Answer Correct ? | 7 Yes | 1 No |
Answer / safeer azam
Capacitors are used to recover the reactive component of
power (part of power utilized for manetization in
windings).It does not matter the source generating the
voltage is Diesel Generator,steam-driven Alternator or any
other source generating A.C supply.Capacitors are always
beneficial on AC supply if the power-factor is maintained
below Unity (using a power-factor regulating relay), on
lagging side.If power-factor is not maintained through
regulating relays then it has the tendency to go on leading
side which means ,over magnetization of windings.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / prn
Kindly do not post nonsense answers, if require go back to
college
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / venkatasubramanian
capacitors are used for produce the inductive power, so that
we can reduce the active power. i.e, genset producing
current is low. Normally when the motor ON some magnetic
field is also produced That magnetic field consume more
current, when we use the capacitor in parallel with the
circuit. It is Balanced.
so capacitor used .9 to .95 (lead/lag) to reduce the
load(producing current) to save the fuel.
By Venkatasubramanian (VVS)
| Is This Answer Correct ? | 1 Yes | 2 No |
which circuit breaker enclosure is best for maintenance guy? 16 bolt & 20 bolt squre or 16,20 bolt hinge
What is the difference between harmored cabled and unharmored cables
kindly send me 11KV MV motor differential protection procedure by primary injection method.
what is the speed of mixie?
where is the primary of CT??
why wave traps are placed only at y and r phase?
In a circuit a capacitor (paper capacitor ) was burned due to over voltage in this case can we replace that type cappacitor with other tye capacitor ?
why can tv operate at low voltage??
why output is out of phase in case of common emitter?
Why is making current of CB always greater than CB breaking burrent?.
what is meant by flywheel and its role in retardation test
Name of Hydrocarbon gases.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)