i have an interview in Qatar Petroleum. So please provide
the all details abt fire & gas systems



i have an interview in Qatar Petroleum. So please provide the all details abt fire & gas syste..

Answer / welcome4ujd

providing all details here is difficult, i will try to give
some basics.

The Fire and Gas system (FGC) is designed to give the
earliest possible warning and location of:
a) A fire in its initial stage.
b) A flammable gas leakage or accumulation up to the
lower explosive limit (LEL%).
c) Any toxic gas likely to be present up to the
occupational exposure limit (OEL).
the architecture is
Detectors(input)--detector interface module--Fire and gas
control panel--outputinterface module--interface relay --
output devices
Description of the items :
1- The detectors are Manual Call Points, Fire
Detectors or Toxic Gas Detectors.
2- All incoming detector field circuitry interface
with the Fire & Gas control panel (F & GCP) by means of a
detector interface modules.
3- The F&GCP (Fire & Gas control panel) looks at all
of the connected Inputs and acts on the information from
certain number of the inputs that agree. This is commonly
known as a 'voting' system.
4- Output interface modules receive the outputs from
the proccessing unit and provide to the output circuits
(Relays)
5- The Interface relay provides electrical isolation
between the plant and fire &Gas control panel and provide
the output devices with the required power for operation.
6- The output devices are either alarms(
audible /optical) and/or control circuits.

Normally a protected plant is divided into fire areas and
each fire area has its own detection, alarm, control and
extinguishing system (if used).
If both fire and gas detection are required, these systems
share common control panels.
The fire detection and alarm system has manually operated
call points and automatic smoke, heat and flame detectors
located in areas where a fire hazard may exist.
Manual initiation of critical control actions overrides any
software-based system.
A brief description of the types of detectors and output
systems is given on the following pages.
The type of a Fir & Gas control panel and associated
detectors/outputs depends on the type of the controller it
self.

Addressable type system
If the controller is intelligent type, the detectors will
be addressable types, which are individually identified at
the F&GCP via a data highway. If the detector is not
addressable type then it is normally connected through a
dedicated interface module located near to the detector.
The addressable detectors and detector interface modules
respond to regular polls from the control panel and report
its type and status on the same loop (normal, alarm, open
circuit, short circuit...etc.).

Traditional type system
If the controller is traditional type (composed of discreet
electronic modules), the detectors are of the traditional
type, which changes the value of the electrical current in
its loop via normal wiring connections.
Each loop is identified on the F&GCP as a Zone.
The zone could include one or more of the traditional
detectors.
The activated detectors can not be individually identified
on the F&GCP, only they can be identified by observing the
integral LED on their locations.

Is This Answer Correct ?    42 Yes 3 No

Post New Answer

More Instrumentation Interview Questions

How to Calibrate Transducers? Can you give me a step by ste procedure?

1 Answers  


Describe how to use megger to measure the earth resistance and insulation resistance

0 Answers  


If we increase D what will be the controller action?

2 Answers  


why I need valve guard and whats different between guard and positioner ??

0 Answers  


How will you measure surface temperature of SUN?

2 Answers   GAIL,






What are different types of control valves?

0 Answers  


Which buffer solution is used for PH transmitter calibration?

3 Answers  


why we use 0.2 to 1.0 kg/cm2 output in control valve

4 Answers   GNFC,


Which topics are covered in Process Control?

0 Answers   Honeywell, L&T,


how can loop single 4-20 ma to two isolation amplifier? i mean i have two isolation amplifier with 4-20 ma input and 1-5 v output.can i done series connection ?

1 Answers  


how ranges is decided for drum level or dearator level,in my pplant i have seen for boiler drum range is -1000 to 1000mmwc, while for dearator -2000 to 0 mmwc ,why they decided to take this range ?

2 Answers  


For crude application in floating roof tank, how to calibrate a DP Transmitter? How is the floating roof weight considered?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)