expalanation for 5p10 class.
Answers were Sorted based on User's Feedback
Answer / anilesh
5p10
5% of error when there is 10 times of current in the
circuit.
Is This Answer Correct ? | 65 Yes | 6 No |
Answer / ravi kaslikar
5P10 means 5% composite Error up to 10 times of rated CT
current. 10 is for ALF ie Accuracy Limit factor. P
indicates Protection class CT.
Is This Answer Correct ? | 37 Yes | 6 No |
Answer / gopalsing
5P10,Means 5%(5P) Of Ration Error Even if 10 Times fo Rated
current pass through the primary of CT
Is This Answer Correct ? | 26 Yes | 4 No |
Answer / arun kumar
10 times of rated primary current injected means 5 percent of composite error is created .
5 - composite error .
P- protection.
10- accuracy limiting factor
these r the standard ALF list - 5 , 10 , 15 ,20 ,30
composite error is related to harmonics
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / grayghostgg
5p10means 5 percentage error and 10 mean ten times the
secondary current the CT can withstand
Is This Answer Correct ? | 3 Yes | 8 No |
Answer / bhanu
"5P 10" in this 5P Accuracy class,10 represents composite
error
Is This Answer Correct ? | 14 Yes | 30 No |
what is the purpose of %impedance for transformer
how does ELR works? explain
what is the k var ratting of 1250kva
Why most of analog o/p devices having o/p range 4 to 20 mA and not 0 to 20 mA ?
Why earthing is required for diesel tank?
is it possible to have dc motors on single chip
Explain what happens to the speed of a series motor as the load decreases
Wat is the best to use in a generator a 6.5kva or a 7 kw
Is the theorem applicable to ac sources?
WHY DOES NEUTRAL DO NOT CARRY EVEN THOUGH IT CARRIES RETURN CURRENT?
One of our gas turbine generator unit "1st stage rotor ground fault" alarm was occured several times. we tried to measure some voltage vulue ground fault protection relay (UNS3020a made by ABB and we measured the value of: Ground: 0.9VDC 5V: 5.8VDC 24V: 23VDC u+: 300 – 350mVAC Rf1: 17.5mVAC Rf2: 17.6mVAC The unit still running and the alarm was reset. As of 6pm yesterday and unitl now no alarm happened again. I our protection relay was defective?
why the difference arise between HT reading & LT reading (submeters fixed in complexes, apartments etc)if the power factos exceed from 0.9 to 1 can the ht meter reads fast?