expalanation for 5p10 class.
Answers were Sorted based on User's Feedback
Answer / anilesh
5p10
5% of error when there is 10 times of current in the
circuit.
| Is This Answer Correct ? | 65 Yes | 6 No |
Answer / ravi kaslikar
5P10 means 5% composite Error up to 10 times of rated CT
current. 10 is for ALF ie Accuracy Limit factor. P
indicates Protection class CT.
| Is This Answer Correct ? | 37 Yes | 6 No |
Answer / gopalsing
5P10,Means 5%(5P) Of Ration Error Even if 10 Times fo Rated
current pass through the primary of CT
| Is This Answer Correct ? | 26 Yes | 4 No |
Answer / arun kumar
10 times of rated primary current injected means 5 percent of composite error is created .
5 - composite error .
P- protection.
10- accuracy limiting factor
these r the standard ALF list - 5 , 10 , 15 ,20 ,30
composite error is related to harmonics
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / grayghostgg
5p10means 5 percentage error and 10 mean ten times the
secondary current the CT can withstand
| Is This Answer Correct ? | 3 Yes | 8 No |
Answer / bhanu
"5P 10" in this 5P Accuracy class,10 represents composite
error
| Is This Answer Correct ? | 14 Yes | 30 No |
In parallel operation time both NGR’s close or not close if both close what will happen
what are the effects of variations in frequency when you are connected to national grid??
whydoes the p.f of diesel generator always be 0.8 explain how will you determine the shortcircuit capacity of network
sir i am ece engineer.i want to job in power plant.what is the best option for me as electrical engineer or instrumentation engineer?pls reply me.
I need a formula to calculate the size of cable as per load but in the terms of length. Please Reply me as i search lot of sites but i did not get the answer.
We are using 3core 11KV HT cable for same phase for generator outgoing, the cable leakage current is high and cable heated overly what is the remidy, if we use the 3core cable for 3phases the problem is solved are not?
what are adantages of OC and SC test over the load test?
what is the rating of Insulation tester for measure 15 KW, 3 phase 415V 50 HZ induction motor?
what is the purpose of using filters in a protective relaying scheme?
what is the safety of ACB & VCB and how can this work and how can the service the ACB & VCB parts name with picture
21 Answers ABB, ACB, Bharti, Claris Lifesciences, Honda, L&T, RotoPower, Sterling Wilson, Wipro,
what is the internal working of star delta starter
what will happen when ac is applied resistor,inductor,capcitor?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)