Why not implimenting power factor in Diesel generator
Answers were Sorted based on User's Feedback
Answer / ravi
In case we correct the existing P.F. in case of DG set by
putting capacitor panel across DG set, then there is no
harm until the cicuit draws inductive or lagging P.F. . But
in case it starts drawing leading P.F. due to addition of
excessive capacitors across D.G. set then the output
terminal voltage would be higher than the induced voltage.
so it is not desirable to operate cap. panel across DG set.
Is This Answer Correct ? | 8 Yes | 1 No |
Answer / rvg.msceb
Offcourse, p.f is the property of load. In a DG set, prime
mover supply mechanical BHP to the alternator, and it does
not depends on the load characterestics, but depends on the
load current.
in short, an alternator demands higher input torque/power
from the prime mover, as soon as current increases from
alternator.
Is This Answer Correct ? | 7 Yes | 1 No |
Answer / bijaya
Yes, we can put capacitors across DG load but it should have a controller ie capacitors should switch on automatically to maintain PF around 0.96 and manual operation of capacitors are not advisable .
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / k.p.sharma
We maintain the P.F. of DG Set approx 0.95 by two methods :-
1.By decreasing the voltage
2.By using power capacitor
Advantage is that for higher PF load current will be low to
deliver the same KW/MW from DG Set.
Is This Answer Correct ? | 4 Yes | 4 No |
Power Factor is the property of load. Generator is a source
of power. So it can not be corrected thru generator. However
Synchronous generators can regulate power factor by
adjusting it's excitation current.
Is This Answer Correct ? | 4 Yes | 6 No |
Answer / vishal
in diesel gen. you adjest p.f. with exitation inc/dicrese
easy.
Is This Answer Correct ? | 0 Yes | 2 No |
how can we check a fully charged battery?
6 Answers BEML, Singareni Collieries,
what will happen when a electric bulb is connected between two phases.it will glow or not
If the load is 10Kw and power factor has to improve from 0.5 to 0.8,how can we select the capacitor rating accordingly.Illustrate by showing formula?
what is the calculation of current when a clampmeter is attached to two phases of any drives.
what is the resistance value of our human body?
Why transformer, generator, ups rating kva?
Why the Transformer connection is changing in different transformer?(Like Star & Delta,Delta & Delta,Star & Star,Delta Star) From that connection where it is used?
What types of CMOS memories have you designed? What were their size? Speed? Configuration Process technology?
0 Answers AFG, Afghan Telecom, GE, IBM, SECL, Sun Pharma, TNPL,
Can you use step up generator transformer of voltage ratio 16.5kv/420kv in place of step up generator transformer 15.75kv / 420 kv
What is the lifetime of a Thyristor? Is there a recommended lifetime for thyristors after which they should be replaced?
why we still use sinusoidal waveforms for transmission and utilisation (we know generation is sinusoidal), instead of other ac waveforms such as triangle, sawtooth, square etc.,? is there any mathematical derivations to prove sinusoidal is efficient than others?
1.why motor rating in kw instead of KVA? 2.why alternators rating in KVA instead of KW?. 3.why transformer rating in KVA instead of KW?.