Answer / ravi
In case we correct the existing P.F. in case of DG set by
putting capacitor panel across DG set, then there is no
harm until the cicuit draws inductive or lagging P.F. . But
in case it starts drawing leading P.F. due to addition of
excessive capacitors across D.G. set then the output
terminal voltage would be higher than the induced voltage.
so it is not desirable to operate cap. panel across DG set.
| Is This Answer Correct ? | 8 Yes | 1 No |
Answer / rvg.msceb
Offcourse, p.f is the property of load. In a DG set, prime
mover supply mechanical BHP to the alternator, and it does
not depends on the load characterestics, but depends on the
load current.
in short, an alternator demands higher input torque/power
from the prime mover, as soon as current increases from
alternator.
| Is This Answer Correct ? | 7 Yes | 1 No |
Answer / bijaya
Yes, we can put capacitors across DG load but it should have a controller ie capacitors should switch on automatically to maintain PF around 0.96 and manual operation of capacitors are not advisable .
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / k.p.sharma
We maintain the P.F. of DG Set approx 0.95 by two methods :-
1.By decreasing the voltage
2.By using power capacitor
Advantage is that for higher PF load current will be low to
deliver the same KW/MW from DG Set.
| Is This Answer Correct ? | 4 Yes | 4 No |
Power Factor is the property of load. Generator is a source
of power. So it can not be corrected thru generator. However
Synchronous generators can regulate power factor by
adjusting it's excitation current.
| Is This Answer Correct ? | 4 Yes | 6 No |
Answer / vishal
in diesel gen. you adjest p.f. with exitation inc/dicrese
easy.
| Is This Answer Correct ? | 0 Yes | 2 No |
for a 132/33kv transformer secondary is star and is connected to NER. and from secondary a cable is running to 33kv swbd. since the cable is single core do i have to run neutral cable also to 33kv swbd.???
is it possible to say motor horsepower number without seeing name plate(when name plate damaged)
What is the most important precaution in any experiment with d.c. Shunt motor?
what is the max load on a 10 mva transformer & plz define it with its formula
what is the working principle of contactor and conditions of normal open and normal close on it?
How will I know that how many batteries I should connect to my UPS unit?
What are the main advantages of generalized error co-efficients?
What is the use of core in the transformer?
HOW TO DO GRID EARTHING IN INDUSTRIES FOR A PRODUCTION BUILDING
while buying 30 kva on line ups for 1 phase ouput, we ave to calculate the number of batteries for 2 hours back up? how to calculate the ah rating and number of batteries
defination of transistor controlled series capacitor
why universal motor work on ac & dc both?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)