Why not implimenting power factor in Diesel generator
Answers were Sorted based on User's Feedback
Answer / ravi
In case we correct the existing P.F. in case of DG set by
putting capacitor panel across DG set, then there is no
harm until the cicuit draws inductive or lagging P.F. . But
in case it starts drawing leading P.F. due to addition of
excessive capacitors across D.G. set then the output
terminal voltage would be higher than the induced voltage.
so it is not desirable to operate cap. panel across DG set.
| Is This Answer Correct ? | 8 Yes | 1 No |
Answer / rvg.msceb
Offcourse, p.f is the property of load. In a DG set, prime
mover supply mechanical BHP to the alternator, and it does
not depends on the load characterestics, but depends on the
load current.
in short, an alternator demands higher input torque/power
from the prime mover, as soon as current increases from
alternator.
| Is This Answer Correct ? | 7 Yes | 1 No |
Answer / bijaya
Yes, we can put capacitors across DG load but it should have a controller ie capacitors should switch on automatically to maintain PF around 0.96 and manual operation of capacitors are not advisable .
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / k.p.sharma
We maintain the P.F. of DG Set approx 0.95 by two methods :-
1.By decreasing the voltage
2.By using power capacitor
Advantage is that for higher PF load current will be low to
deliver the same KW/MW from DG Set.
| Is This Answer Correct ? | 4 Yes | 4 No |
Power Factor is the property of load. Generator is a source
of power. So it can not be corrected thru generator. However
Synchronous generators can regulate power factor by
adjusting it's excitation current.
| Is This Answer Correct ? | 4 Yes | 6 No |
Answer / vishal
in diesel gen. you adjest p.f. with exitation inc/dicrese
easy.
| Is This Answer Correct ? | 0 Yes | 2 No |
sometime battery charged and then automatically charged when rectifier ON conition, is there any chances please clarify the same.
why Copper loss is represented as I square R ?
11 kg trivevter meter has rating of -/5amps. And pt ratio11000/110v and is connected with 11kv ct/pt unit of cr ratio 75/5amps. And pt ratio of 11000/110v while checking accuracy of meter with HT Accuchek meter what value of PT ratio and CT ratio to be filled in Accuchek meter
what is the role of reactive powerin transmission and distribution?
in case of induction motor when overload condition or any short ckt. why stator winding burn not to be rotor winding
Is the theorem applicable to ac sources?
What are the protections for safe running of electric generator?
Transformer TTR test procedure
DEAR SIR/MADAM,CLEARLY EXPLAIN ABOUT CRAWLING AND COGGING EFFECTS IN INDUCTION MOTOR.
What is function of condenser in fan?
Do these factors (settling time, peak time, steady state error, overshoot, rise time, MPOS (Maximum percent over shoot)) are the part of first order, second order, higher order, linear, non-linear, open-loop, closed-loop, homogeneous & non-homogeneous systems ?
list down a few application of ac & dc in a generating station?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)