Transformer TTR test procedure
Answers were Sorted based on User's Feedback
Answer / vimal m
Transformer Ratio Test
The performance of a transformer largely depends upon perfection of specific turns or voltage ratio of transformer. So transformer ration test is an essential type test of transformer. The voltage should be applied only in the high voltage winding in order to avoid unsafe voltage.
Procedure of Transformer Ratio Test
First, the tap changer of transformer is kept in the lowest position and LV terminals are kept open.
Then apply 3-phase 415 V supply on HV terminals. Measure the voltages applied on each phase (Phase-phase) on HV and induced voltages at LV terminals simultaneously.
After measuring the voltages at HV and LV terminals, the tap changer of transformer should be raised by one position and repeat test.
Repeat the same for each of the tap position separately.
The above transformer ratio test can also be performed by portable transformer turns ratio (TTR) meter. They have an in built power supply, with the voltages commonly used being very low, such as 8-10 V and 50 Hz. The HV and LV windings of one phase of a transformer are connected to the instrument, and the internal bridge elements are varied to produce a null indication on the detector.
Is This Answer Correct ? | 0 Yes | 0 No |
this is a special test.refer to manufacturer.
Is This Answer Correct ? | 2 Yes | 4 No |
why ct ratio always rated 5.
What is mean 2XWY
what causes contact chatter when there is no demand on the air conditioning unit?
what is the working principle of smoke detector in fire alarm system
Difference between on line capacitor and Station type capacitor
Is it possible to protect 3phase overload and earth fault of the 3phase system using two CT's.
WHAT IS THE DIFFRENCE BETWEEN EARTHED AND UNEARTHED CABLE (XLPE)?
L.A. (Lightening Arrester) is located at a place from where transmission line enters the transmitting substation. So L.A. (Lightening Arrester) is the first equipments which has to encounter with lightening, high voltage surges and switching surges. It has to absorb energy of lightening, high voltage surges, and switching surges. L.A. (Lightening Arrester) is made up of layers of semiconductors. If these layers can not tolerate energy released by lightening, high voltage surges, and switching surges the L.A. (Lightening Arrester) blasts.
How to assume answer to electrical questions
solar inverters was not connected to the nuteral link .this nutwral possible to any other systems
In power plants the reading changes abruptly to give value (MW -25) (MVAR -15) What are the reasons for this? What is the solution?
what is the disadvantages of common earthing for AC and DC equipment? (i am talking about inverter control room and inverter duty transformer earthing is common...?)