Answer / vimal m
Transformer Ratio Test
The performance of a transformer largely depends upon perfection of specific turns or voltage ratio of transformer. So transformer ration test is an essential type test of transformer. The voltage should be applied only in the high voltage winding in order to avoid unsafe voltage.
Procedure of Transformer Ratio Test
First, the tap changer of transformer is kept in the lowest position and LV terminals are kept open.
Then apply 3-phase 415 V supply on HV terminals. Measure the voltages applied on each phase (Phase-phase) on HV and induced voltages at LV terminals simultaneously.
After measuring the voltages at HV and LV terminals, the tap changer of transformer should be raised by one position and repeat test.
Repeat the same for each of the tap position separately.
The above transformer ratio test can also be performed by portable transformer turns ratio (TTR) meter. They have an in built power supply, with the voltages commonly used being very low, such as 8-10 V and 50 Hz. The HV and LV windings of one phase of a transformer are connected to the instrument, and the internal bridge elements are varied to produce a null indication on the detector.
| Is This Answer Correct ? | 0 Yes | 0 No |
this is a special test.refer to manufacturer.
| Is This Answer Correct ? | 2 Yes | 4 No |
What is the tests required for a 132 kV, 400 kV , 765 kV for a Circuit Breaker and Power Transformer before commissioning ?
0 Answers Eprosys Engineering Consultants,
explain working of differential protection for a transformer?
What is Procedure the procedure to select CT's & PT's in 66kV and above substation
block diagram of 2 ups system connected in hot stand by mode?
how will you determine the short circuit capacity of a network
How many companies are manufacturing 33 KV HT Breaker
please send the IS strandard for electrical to sakthi_murugan86@yahoo.co.in
can i connect the two phases of scott connected transformer,if not why?
I HAVE BEEN SELECTED FOR APGENCO A.E(ELECTRICAL) 2008.HOW MUCH WEIGHTAGE FOR INTERVIEW AND WRITTEN TEST.HOW I HAVE TO PREPARE. PLEASE GIVE INFORMATION IF U KNOW.WHAT ABT G.D THIS TIME.CALL RATIO 1:2
Single line digram for 11 kV to distribution use go,la and do
if we have 320KVA Genset kindly advice how much load we can put it.
what is thyristor, how is it works
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)