How does a star connection and delta connection work? How
does the star connection save starting current and how does
it change to delta?
Answers were Sorted based on User's Feedback
Answer / pillay
A typical 3 phase motor has 3 sets of windings. Each set of
windings have 2 terminals namely the start and the end of
the winding.During the start the end of of all 3 windings
is joined together through a contactor known as the star
contactor and the 3 phase power supply is applied across the
start terminals of the 3 windings.This windings are actually
designed for the application of 2 different phase voltages
across them.So during start up lower voltage is applied and
so a lower current is drawn. but after a few seconds the
connections are changed through the change over of
contactors to the full voltage across the windings known as
delta connections. This start and change over is done by
timer controlled contactors.
| Is This Answer Correct ? | 6 Yes | 4 No |
Answer / hiren bhatt
in star connection line voltage of system is decreased to 1
by square root of 3 is equal to 1/1.73 of line voltage,
thats why in starting motor get reduced voltage asper this
ratio and hence star connection help to reduce effect of
dv/dt to the connected load and hence its insulation and
starting current protected
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / devi kumar
star resistance have more than delta resistance ex:star have 4 ohms delta 2 Ohms so I=V/R star current =230/4 57.5
Delta current = 230/2 = 115
| Is This Answer Correct ? | 1 Yes | 0 No |
Will a 230VAC motor run OK at 208VAC.
How do you select the pickup value of the relay?
where can the transformer having vector group Yny0 be used??
0 Answers GK Power, NEA, Petrotech,
What is broken wire condition in transmission line?
what is the function of switch gear ?
Electrical Diagram of Electric Arc Furance from transformer to Furances
Let me know that how i calculate the alternator sub tranciant reactance and tranciant reactance.
What is cable gland,why does use for?
what is ht breaker
in power generator normaly voltagr betwween esth to neutral is 0 but my work place generator show the volatge is 60v any body know why? thanks
how to do the ductor test?
In response to Mr Bikas. If fault current is 52 kA then what will be the CT specification
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)