We use MCCB not MCB for motor starters because MCCBs has capablity to drawout the motor starting current which is 5-6 times the full load current of motor for 1sec.
Then why we use SDF in starter panel means MCC panels.
Pls reply if any one knows this answer.
Answer / omer a.osman
What do you mean by SDF. I guess Star/Delta.
In this case, the starting current will be reduced & within 15 to 20 Sec. the Sytem will changed to Direct on line in running Condition by taking the full load current. Hence, the recommended MCCB rating as protective device to protect the feeders should not be less than the current carrying capacity & tripping current about 1.45In. However, the breaking Capacity of the MCCB is an essential factor.
| Is This Answer Correct ? | 0 Yes | 0 No |
why neutral busbar size is half of the phase busbar size in control panels
What is the safety of UPS?
watt meter have 4 terminals what there name??? and what theses 4 terminals indicates ?? and why 2 terminals are short circuited??
what parameters should we check to reduce the power bill
which starter is used for synchronous motor
how to testing the AC 3 phase motor? and what is the test procedure & kits required for testing?
do we use neutral grounding for resistive balanced load? if we use what happen?
which motor is used in our Indian Ceiling fan -Capacitor start and run or Capacitor start? (during repair i saw only one capacitor so it should be start only)
5 Answers ABB, Bajaj Electricals, Power Grid, Ruchi Soya, Suzuki,
I HAVE BEEN SELECTED FOR APGENCO A.E(ELECTRICAL) 2008.HOW MUCH WEIGHTAGE FOR INTERVIEW AND WRITTEN TEST.HOW I HAVE TO PREPARE. PLEASE GIVE INFORMATION IF U KNOW.WHAT ABT G.D THIS TIME.CALL RATIO 1:2
what is Wave Trap? And its Function ? Detail? Where it is Used?
What is ZCT? it operating principle and how is work with RCCB (residual current circuit breaker)?
This is about the recent problem that we have faced in our project site. We have 6/7.5 MVA. 66/11kV three phase star - star power transformer. The neutral was solidly connected to the earthing mat. But because of high resistance of earthing mat (130 ohm on LV and 180 ohm on HV), one day LV side neutral earthing conductor melted and we had a huge damage. Can any one plz tell me what might happen when we connect power transformer neutral to the earthing mat which has high resistance (>100 ohm ) ?????
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)