What is the out put of a CT? How the ratio is decided ?
Answer / mojinkoshy
The O/P of a current transformer (CT) is normally the secondary current of the CT. For eg.the CT may be rated like this "60/5A 15VA CL-1", in which 60/5A means the CT’s primary side current is 60A & the secondary side is 5A, 15VA means burden of the CT ie. Maximum power capacity / rating, CL-1 means the insulation class of the CT.
Since the O/P of CT’s are used for protection / measurement, the o/p rating is totally depends up on the ratio settings of the protective devices tripping capacity or that of the measuring instruments measurement capacity .
Is This Answer Correct ? | 5 Yes | 0 No |
If the load of transformer is getting more than its rating,,,than how to overcome this problem? Suppose thee rating of transformer is 315kva and the load is going beyond than the rating say around load: 352kva... Than how can we solve this problem without deducting the load.
what is pole slip ?
what is inter connected dc generator?
0 Answers Lovely Professional University,
how to select cable size for three phase?
Write down the brushes of a de machine.
what is inductance function?
How to Calculate KA Rating of Main LT Panel
why transformer neutral and CT Secondary neutral is connected to earth?
what is the difference between home inverter and online ups?
I have a relay contact rated at 220v dc which is supplied with a 24vdc from the panel,for it to trip the dampers(24vdc).What if the application of the relay changes so that it should work at its rated 220vdc then will it work at 24vdc supply given or any other consideration needs to be taken .....
What is sensitivity of a measurement?
what is the differebt between ac and dc fuse?