Answer / shonali
LLL or 3phase fault is most severe fault than the LG OR LL
or other unsymmetrical faults. 3phase or symmetrical fault
is a sudden short circuit produces currents and voltages
which are transient in nature before they settle down
| Is This Answer Correct ? | 125 Yes | 25 No |
Answer / bhuvanagiri ramesh
LG fault is most severe fault at the alternator terminals than three phase fault, because zero sequence reactance is less at the generator and fault current incase of LG fault is three times the positive sequence current. As the fault location moves away from alternator zero sequence reactance increases and three phase fault becomes more severe.
| Is This Answer Correct ? | 62 Yes | 13 No |
Answer / amritesh pandey
lll faults are most sevre but if lg fault occurs very close to
the generator terminals then it is the most dangerous fault....
| Is This Answer Correct ? | 30 Yes | 8 No |
Answer / gunasekaran
LLL fault is more danger than other fault.because large
fault current than other fault
| Is This Answer Correct ? | 35 Yes | 22 No |
Answer / akhilesh
actually l-g fault is severe at generator and l-l-l-g is severe at line.. becoz when derz l-g fault at gen .. 1.5i flows through other two phases instead of i, which is dangerous.
At lines suppose l-l-l-g occurs.. then becoz of zero voltage at tht place.. the high potential difference will make very high current to flow through lines.. which is again severe. from the formulas.. this value is more than any other current flowing through lines
| Is This Answer Correct ? | 19 Yes | 7 No |
Answer / yogesh rathod
LG fault is more severe at the generator side.
otherwise LLLG fault is more severe.
| Is This Answer Correct ? | 16 Yes | 5 No |
Answer / shashi
LLL fault is more sever than all other faults usually. But LG fault is more dangerous when generator is solidly grounded because at this condition LG fault current flows 1.5 times of three phase LLL fault current.
| Is This Answer Correct ? | 8 Yes | 1 No |
Answer / harshal nemade
as symmetrical fault that is L-L-L is more dangerous. but if we calculating the fault current the LG fault current is very large as compared to other fault so from this we can conclude that LG fault is more severe than other fault.
as LG fault is take place between line and ground and ground potential is assume as zero and also having zero impedance so this fault current is very larger which is 1.5 time L-L-L fault. so according to this theory LG fault is more severe than other fault.
| Is This Answer Correct ? | 4 Yes | 3 No |
Answer / aviya
In transmission line LLG fault is the most severe.
In sync m/c LG fault is the most severe.
| Is This Answer Correct ? | 0 Yes | 4 No |
what is threshold voltage for a relay???what does it exactly means ?whats its value in our indian transmission system say 11kv feeder RMU relay
What is a signal flow graph?
how would you determin the horsepower of a motor without a nameplate
why the manufacturer provide M and C terminals ? why they will not internally short them ?
when we use neutral line as grounding.
Pls anyone explain me the basics of wiring a house?
what is the working of ups.
What are the weight of 800KV DA,DB and DC type tower ?
What happens if we give the supply to the rotor of induction motor and make its terminal shorted?
why the neutral line is not giving shock to us if we touch it ?
IF i have switchgear with busbar current rating of 1000Amp 35kA then is it necessary to have outgoing breaker kA rating to be equal to busbar kA rating?
wat is the difference between real power and reactive power..which is useful..?and how it s useful..wat is the effect of these on a power system...
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)