lllg,llg,ll,lg,lll which fault is severe and why?
Answers were Sorted based on User's Feedback
Answer / shonali
LLL or 3phase fault is most severe fault than the LG OR LL
or other unsymmetrical faults. 3phase or symmetrical fault
is a sudden short circuit produces currents and voltages
which are transient in nature before they settle down
Is This Answer Correct ? | 125 Yes | 25 No |
Answer / bhuvanagiri ramesh
LG fault is most severe fault at the alternator terminals than three phase fault, because zero sequence reactance is less at the generator and fault current incase of LG fault is three times the positive sequence current. As the fault location moves away from alternator zero sequence reactance increases and three phase fault becomes more severe.
Is This Answer Correct ? | 62 Yes | 13 No |
Answer / amritesh pandey
lll faults are most sevre but if lg fault occurs very close to
the generator terminals then it is the most dangerous fault....
Is This Answer Correct ? | 30 Yes | 8 No |
Answer / gunasekaran
LLL fault is more danger than other fault.because large
fault current than other fault
Is This Answer Correct ? | 35 Yes | 22 No |
Answer / akhilesh
actually l-g fault is severe at generator and l-l-l-g is severe at line.. becoz when derz l-g fault at gen .. 1.5i flows through other two phases instead of i, which is dangerous.
At lines suppose l-l-l-g occurs.. then becoz of zero voltage at tht place.. the high potential difference will make very high current to flow through lines.. which is again severe. from the formulas.. this value is more than any other current flowing through lines
Is This Answer Correct ? | 19 Yes | 7 No |
Answer / yogesh rathod
LG fault is more severe at the generator side.
otherwise LLLG fault is more severe.
Is This Answer Correct ? | 16 Yes | 5 No |
Answer / shashi
LLL fault is more sever than all other faults usually. But LG fault is more dangerous when generator is solidly grounded because at this condition LG fault current flows 1.5 times of three phase LLL fault current.
Is This Answer Correct ? | 8 Yes | 1 No |
Answer / harshal nemade
as symmetrical fault that is L-L-L is more dangerous. but if we calculating the fault current the LG fault current is very large as compared to other fault so from this we can conclude that LG fault is more severe than other fault.
as LG fault is take place between line and ground and ground potential is assume as zero and also having zero impedance so this fault current is very larger which is 1.5 time L-L-L fault. so according to this theory LG fault is more severe than other fault.
Is This Answer Correct ? | 4 Yes | 3 No |
Answer / aviya
In transmission line LLG fault is the most severe.
In sync m/c LG fault is the most severe.
Is This Answer Correct ? | 0 Yes | 4 No |
Who many reason of ignition fail ?
in my industry we are using 3 step up transformers for induction heaters..i.e 415/580v and other are 11/440v.in power consumption does a step trnsformer makes any difference compared to step up?? plz explain
Hi everyone, I'm Lachuu, recently joined automation company as PLC Engineer. I have certain basic question, I request all big gurus and seniors to answer these question. Because this will be very helpful to me as well starters like me. How to design a control circuit (ex: pick & place - my current project) Yamaha robot PxYx series controller RCX222, using 6 cylinder double acting, plc keyence kv p16r 2 expansion unit for input and output each. How to select panel terminal mcb elcb powersupply. My main concern in some projects how to select dc power supply, mcb rcb(I came across dif bt b c d curves, but stil confusing, pls help me :-(. I would really appreciate all who are going respond to this question.
How many methods to take IR value of Current Transformer?
why the earth is taken minimum in supplying? wather it the proportional factor to getting work any equipment or a power plant?
3ph line voltage 220v, how can run a 220v single ph motor or Light?
State the points to be considered for selecting a particular type wiring.
what is suitable alternative for an igbt?
what are corona losses
What is thyristor?
Wat wil happen if Transformer is operated at 100 HZ Frequency?
WHY THE COLOR OF OUTDOOR TRANSFORMER IS BLUE ONLY???