Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


lllg,llg,ll,lg,lll which fault is severe and why?

Answers were Sorted based on User's Feedback



lllg,llg,ll,lg,lll which fault is severe and why?..

Answer / shonali

LLL or 3phase fault is most severe fault than the LG OR LL
or other unsymmetrical faults. 3phase or symmetrical fault
is a sudden short circuit produces currents and voltages
which are transient in nature before they settle down

Is This Answer Correct ?    125 Yes 25 No

lllg,llg,ll,lg,lll which fault is severe and why?..

Answer / bhuvanagiri ramesh

LG fault is most severe fault at the alternator terminals than three phase fault, because zero sequence reactance is less at the generator and fault current incase of LG fault is three times the positive sequence current. As the fault location moves away from alternator zero sequence reactance increases and three phase fault becomes more severe.

Is This Answer Correct ?    62 Yes 13 No

lllg,llg,ll,lg,lll which fault is severe and why?..

Answer / amritesh pandey

lll faults are most sevre but if lg fault occurs very close to
the generator terminals then it is the most dangerous fault....

Is This Answer Correct ?    30 Yes 8 No

lllg,llg,ll,lg,lll which fault is severe and why?..

Answer / gunasekaran

LLL fault is more danger than other fault.because large
fault current than other fault

Is This Answer Correct ?    35 Yes 22 No

lllg,llg,ll,lg,lll which fault is severe and why?..

Answer / akhilesh

actually l-g fault is severe at generator and l-l-l-g is severe at line.. becoz when derz l-g fault at gen .. 1.5i flows through other two phases instead of i, which is dangerous.
At lines suppose l-l-l-g occurs.. then becoz of zero voltage at tht place.. the high potential difference will make very high current to flow through lines.. which is again severe. from the formulas.. this value is more than any other current flowing through lines

Is This Answer Correct ?    19 Yes 7 No

lllg,llg,ll,lg,lll which fault is severe and why?..

Answer / yogesh rathod

LG fault is more severe at the generator side.
otherwise LLLG fault is more severe.

Is This Answer Correct ?    16 Yes 5 No

lllg,llg,ll,lg,lll which fault is severe and why?..

Answer / shashi

LLL fault is more sever than all other faults usually. But LG fault is more dangerous when generator is solidly grounded because at this condition LG fault current flows 1.5 times of three phase LLL fault current.

Is This Answer Correct ?    8 Yes 1 No

lllg,llg,ll,lg,lll which fault is severe and why?..

Answer / harshal nemade

as symmetrical fault that is L-L-L is more dangerous. but if we calculating the fault current the LG fault current is very large as compared to other fault so from this we can conclude that LG fault is more severe than other fault.
as LG fault is take place between line and ground and ground potential is assume as zero and also having zero impedance so this fault current is very larger which is 1.5 time L-L-L fault. so according to this theory LG fault is more severe than other fault.

Is This Answer Correct ?    4 Yes 3 No

lllg,llg,ll,lg,lll which fault is severe and why?..

Answer / aviya

In transmission line LLG fault is the most severe.
In sync m/c LG fault is the most severe.

Is This Answer Correct ?    0 Yes 4 No

lllg,llg,ll,lg,lll which fault is severe and why?..

Answer / suneetha

line-grnd fault is most severe fault.It is seen that usin
formula lg current is almost 1.5 times greater than three
phase fault(symmetrical fault)

Is This Answer Correct ?    14 Yes 61 No

Post New Answer

More Electrical Engineering Interview Questions

what is threshold voltage for a relay???what does it exactly means ?whats its value in our indian transmission system say 11kv feeder RMU relay

3 Answers  


What is a signal flow graph?

0 Answers  


how would you determin the horsepower of a motor without a nameplate

3 Answers  


why the manufacturer provide M and C terminals ? why they will not internally short them ?

1 Answers  


when we use neutral line as grounding.

1 Answers  


Pls anyone explain me the basics of wiring a house?

3 Answers  


what is the working of ups.

7 Answers  


What are the weight of 800KV DA,DB and DC type tower ?

0 Answers   L&T,


What happens if we give the supply to the rotor of induction motor and make its terminal shorted?

2 Answers  


why the neutral line is not giving shock to us if we touch it ?

0 Answers   GPREC,


IF i have switchgear with busbar current rating of 1000Amp 35kA then is it necessary to have outgoing breaker kA rating to be equal to busbar kA rating?

6 Answers   L&T,


wat is the difference between real power and reactive power..which is useful..?and how it s useful..wat is the effect of these on a power system...

10 Answers   ABB,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)