why we are using panel space heaters in different control
schemes????
Answers were Sorted based on User's Feedback
Answer / abhishek
panel space heater is used for removing the moisture due to
which insulation breakdown may occur
Is This Answer Correct ? | 17 Yes | 2 No |
Answer / ilononurb
panel space heater is used to drying up the moisture
entered in the panel to avoid surface leakage current which
may affect the insulation dielectric strenght of the
insulator failure that may cause of series and shunt fault
in the system.
Is This Answer Correct ? | 8 Yes | 2 No |
Answer / xyz
PANEL SPACE HEATERS ARE NOT A MUST THESE ARE GENERALLY
PROVIDED IN EUROPEAN COUNTRIES AS THIER CLIMATE IS VERY
COLD AS COMPARED TO OURS.BUT AS WE ARE INDIANS WE BLINDELY
TEND TO FOLLOW THERE CONFIGURATION AND SO WE DO........EVEN
IF NOT NECCESORY AND THATS WHY THIS WAS ASKED............
Is This Answer Correct ? | 2 Yes | 0 No |
How to maintaine ht motor efficiancy
What the purpose of transient fault recoredr in substation
what is the role of impedance in transformer?based on secondary f.l.current(139 amps) and impedance(4.07) of 415/415v of 100 kva transformer. what is the primary current?
In A.C systems, fuse is placed in phase-in order to disconnect the circuit during faulty condition. But, what is the reason for putting "LINK" in neutral istead of connecting through (same) wire.
how to calculate the settings for shaft ct protn in hydro generators
working principle of AC Servo Motor with its construction
Why in 6 KV XLPE cable termination kit used and why not in 380 V xlpe cable same is not used
3phase motor can be used as a Prime mover for alternator.
How to test transformer
what is slip ring startor
Explain how you intend to work under pressure to meet up with deadline target?
how to identified power tranfer line is how much KV????