Answer / shonali
there is no CW and CCW synchronization it depends on the
speed difference
synchronization is connecting our generator to grid by
matching with the grid frequency.
a synchroscope is used if our generator speed is less than
grid speed (frequency) the synchroscope rotates counter
clock wise (lag).
if our speed is high the scope needle rotates CW (lead)
if it is equal the needle stops
| Is This Answer Correct ? | 21 Yes | 6 No |
Answer / jock
To ensure the incoming generator takes up load as soon as
the generator circuit breaker is closed.
If synchronism was achieved with the synchroscope
indicating an anti-clockwise rotation the generator would
not take up load and instead would driven by the bus, ie.
reverse powered. If the reverse power is large enough
tripping of the generator is likely to occur.
When manually synchronising a generator to the bus it is
normal to give a quick 'increase' command on the controls
just after the breaker closes to ensure positive power
loading takes place.
| Is This Answer Correct ? | 8 Yes | 1 No |
Answer / amritpal singh sidhu
I think this is due to the phase sequence, because we use
the sine wave in electrical generation so the sine wave
produced is according to quadrants(In which sine wave is
plotted CLOCKWISE ).
| Is This Answer Correct ? | 10 Yes | 4 No |
Answer / vikas wadhwa
In my point of view; in modern turbo-generators there is
already provision of about 5% automatic load command as
soon as gen. breaker is closed thus leaving no chances of
gen. tripping on reverse power. Hence, it will not make any
difference technically whether syncronization is done in
cloclwise or anticloclwise direction.
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / anees ur rehman
I hope that answer 2 and 4 are v.good.Normally
synchronisation done at 1/10 frequency of incoming
generator kept higher thans the exisisting source.why.yes
when it is synchronised as generator take load its speed
decreases due to low frequency it will trip so its
frequency is kept 1/10 times more than source
| Is This Answer Correct ? | 5 Yes | 3 No |
Synchronization should be done in CW direction , to avoid reverse power trip , because CW means your alternator speed and voltage is slight greater then grid ,after immediate synchronizing load will delivered to grid , other wise there is change of reverse power trip.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / sheena mahany
i didnt get anything . be a little bit more clear....
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / manav
There are five conditions that must be met before the
synchronization process takes place. The source (generator
or sub-network) must have equal
line voltage, frequency, phase sequence, phase angle, and
waveform to that of the system to which it is being
synchronized.
(source:----wikipedia)
Clockwise mode of operation is a standard.It has been set to
ensure that phase sequence is not reversed while
synchronizing the generators. Otherwise, same thing might
happen as explained in Answer #7.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / mukul
synchronisation is done in CW direction coz generator should have voltage slightly more than tha system .. because at tha time of synch system start taking load from generator instantly. to avoid generator speed lower than the rated one this needs to do.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / p.anandsah
It doesn't matter if you synchronise TG with Grid in cw or anti cw . Just after synchronisation increase the power as soon as possible.
| Is This Answer Correct ? | 0 Yes | 0 No |
What will happen if i used 11KV earth ht kit to 11 KV / 11 KV cable termination?
what are the changes made in induction motor so that it act as induction generator
If 100 KAV USP dedicated earth got disconnect / Cut. What will happen at load.
A wattmeter is marked 15 A/30A, 300V/600V and its scale is marked up to 4500 watt. When the meter is connected for 30A, 1600V, the pointer indicates 2000 watts. The actual power in the circuit in
what do u understand from filter factor of reactor?
what is practical efficiency of power transformer..?
What is synchro?
how we can come to know that motor winding resistance which showing by DMM is right or wrong???is there any chart or something that we will compare & check???
Differentiate between real and apparent power?
why mccb is not tripping when phase & neutral terminal are interched ?
Why line VTG = √3 phase VTG in star? How?
0 Answers Endurance International Group, Infosys,
check list of maintenance of transformer?
11 Answers ABC, Cosmos, EPRON, Essar, Godrej, Hescom, Infosys, KPTCL, TCS,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)