What happen if LV supply is fed to a HT motor?

Answers were Sorted based on User's Feedback



What happen if LV supply is fed to a HT motor?..

Answer / m.anand

if we connect an ht motor with LT supply the motor run
according the magntic field produced by them.and then also
the torque developed by the LT supply is much lesser than
the torque devloped the HT supply.for example if we pull a
load with 100% of energy is not equal when we pulling the
same load of 20% of energy

Is This Answer Correct ?    2 Yes 0 No

What happen if LV supply is fed to a HT motor?..

Answer / shubh

If LT supply is fed the motor will start with a slow speed
but slowly and surely it will reach the required spped

Is This Answer Correct ?    2 Yes 1 No

What happen if LV supply is fed to a HT motor?..

Answer / mahesh meshram

If HT motor fed on LT supply, motor will run slowly and speed will increase with time. Initially motor will draw app. 1/3rd of the rated current and it will also reduce by 2-5 amp and will get steady.Motor such type of performance is expected only if it's bearing, rotor and other factors are good.

Is This Answer Correct ?    0 Yes 0 No

What happen if LV supply is fed to a HT motor?..

Answer / atta

HT MOTOR WILL NOT RUN DUE TO LOWER MAGNETISING EFFECT

Is This Answer Correct ?    0 Yes 1 No

What happen if LV supply is fed to a HT motor?..

Answer / singaravelu

There is no problem on it's winding and it's torque and it's rpm will reduced and it will runs at a short duration minimum one hour continusously it will runs there is chases to coil burn.It will held to test the Motor and find it's housing problem.

Is This Answer Correct ?    0 Yes 1 No

What happen if LV supply is fed to a HT motor?..

Answer / ankur

As power taken by motor is VIcos@, so if less voltage will
be applied on the motor then in order to develop magnetic
field in the motor i.e in between rotor & stator, it will
take large current as compared to it rated current, result
in over heating of winding, excess losses, and finally
winding will burn out.

Is This Answer Correct ?    2 Yes 4 No

What happen if LV supply is fed to a HT motor?..

Answer / ramya sree

Hv windings are designed such that they have more number of
turns to get high voltage, also less thickness as it carries
less current.comparitively, Lv windings are designed such
that they have less turns and more thickness so that they
withstand high current. when such high current is passed
through hv winding, being thin it cannot withstand such high
current,due to heat developed, winding may burn.

Is This Answer Correct ?    0 Yes 2 No

What happen if LV supply is fed to a HT motor?..

Answer / mohit kochhar

if LT applied to HT motor then motor winding will burn out.
because motor current is inversely propotional to voltage.
i f applied less voltage the motor current will increase.
e.g.
1500 kw motor supply voltage 6.6 kV current 155 A.
if applied 415 V then current is around 2000A .

Is This Answer Correct ?    26 Yes 63 No

What happen if LV supply is fed to a HT motor?..

Answer / vikramsena_reddys

motor winding will fail under low voltage.

Is This Answer Correct ?    16 Yes 58 No

Post New Answer

More Electrical Engineering Interview Questions

WHY R USE IN BRUSH IN THE MOTOR?

6 Answers   L&T,


HOW DO YOU PROVE THE HIGH VOLTAGE CABLES OR BUSBAR IS DEAD EVEN AFTER IT IS DE ENERGISED

6 Answers  


While HT line put on to activate ACB in low tention panel VCB tripping instantly.why it happens

0 Answers   Engineering,


what can i do line to line fault

4 Answers  


how to calculate KA rating of C.B?explain with Formula.

1 Answers  






distribution is maximum done by a)radial b)network c) parallel d)b & c

0 Answers  


Define ampere

0 Answers  


what is maximum or Threshold value of current 7 voltage that a common man can withstand

1 Answers  


what is the value of combined earthing in general electrical circiut?

0 Answers   Cathtect Engineering,


How to Calculate Contracted Maximum demand using motor Hp or Current

3 Answers  


Draw an S.L.D of the main panel for a hospital, showing meter position. Essential loads are: 1) Equipment load 100 KW 2) Critical load 500 KW 3) Life AID Safety load 400 KW 4) NON-Essential load 200 KW 5) Other service loads 200 KW Calculate and suggest the size of the transformer, size of main cable, capacitor bank, and calculate the capacity of an emergency load having above first three mentioned loads is supplied by an emergency generator.

0 Answers   FEWA, HMK,


Is it a better option to procure screw type air compressor rather than reciprocating air compressor?If so, what is the reason?How should we select an air compressor(100 CFM)? Please mention the important parameters of air compressor.

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)