megger generates D.C. voltage while earth tester generates
A.C.voltage is it true? I know for megger it is D.C
generator but what about earth tester?
Answers were Sorted based on User's Feedback
Answer / hariprasanna
megger is used to measure insulation resistance (mohm)of let transformer ..so to do this we have to connect it to the body of transformer and windings ,so if we use ac then there will be probability of dielectric change and discharge,so we use dc in megger to get a constant supply...but in earth tester it is uesd to measure earth resistance ,if we use dc hear then as nwe know earth contain metals,chemicals..so due to electrolysis corrosion will start around earth electrode..so to aviod this we use ac ..
Is This Answer Correct ? | 21 Yes | 0 No |
Answer / anindya chitta bagchi
true,earth tester generates ac voltage.
Is This Answer Correct ? | 11 Yes | 3 No |
As per my knowlegde there is no much diffrence between
megger and earth megger.megger is used to measure
insulation resisitance(mega ohm)and earth megger is used to
measure earth resistance(ohms).constructionally there is no
difference.both contains an in built permanant magnet hand
driven generator.The difference lies in the no of
terminals.megger contains 3 and earth megger contains 4
terminals.Both will generate dc voltage only during
measurement.
Is This Answer Correct ? | 22 Yes | 15 No |
Answer / avinash
Megger and Earth tester have opposite functions. Megger check insulation resistance to make sure there is no path to Earth, and it measure the resistance in Mega ohms. Megger uses DC to avoid conductance due to reactive components.
Earth tester function makes sure there is very good path to Earth and measures resistance in fraction of ohms. It uses AC to make sure there is no inductance in path. With DC inductance can give false zero reading.
Is This Answer Correct ? | 1 Yes | 1 No |
how much current in live 11 Kv distribution Line?
I have 10 amp MCB for my air conditioner of 1.5 ton capacity. When I connect the ac direct it is started running but when connected through stabliser the Mcb Get trip and air conditioner couldn't start.please confirm whether Mcb is required to be upgraded to 20 amp. There is no fault in ac and the stabliser. Please advice the reason of tripping the mcb when connected through the stabliser.
wath is skin effect?
What is the major differences between RCCB & ELCB? If we use ELCB of less sensitivity why does it trip often and can we control it from tripping?
As you achieve greater success with the company after some years, Will you like to be a share holder in our company?
What is high frequency grounding????Applications........
what is bausbar?
what is the difference between Resistance VS capacitance
Can someone explain how does an IDMT relay works.
what is the k var ratting of 1250kva
Why resistance is not measure in running conditions of motor
In a transformer ,when voltage decreases current increases. but this is a violation of oms law.why?