Answer / subash nishad
in distribution transformer we are using delta/star
configuration because many consumers having single phase
load .for this one phase and neutral is nessesary. from
delta / star configuration we can get neutral.
delta/ star is correct.
Is This Answer Correct ? | 16 Yes | 0 No |
Answer / dhiraj
delta/star
bcoz from secondary star we can get neutral
Is This Answer Correct ? | 10 Yes | 2 No |
Answer / naresh kumar
we use delta star connection because Zero sequence currents
will not enter into grid which is connected to high voltage
side of transformer(delta side).
Is This Answer Correct ? | 3 Yes | 1 No |
Why do we avoid electrical conduits in floors at apartments?
HOW DO I CALCULATE OVER LOAD RELAY & CONTACTOR IN DOL STARTER? & in dol why it is require circuit breaker?
iam interesting to design the control panel for 3 phase pump motors by controling single phase switches.iam plan to use fuse,contactor & relay for motor protection .how can i select the voltage & amps rating for fuse,contactor & relay plz guide me .if anybody clarify my doubt means it will more helpful for my future .
there is a # KVA Transformer of 11 KV/440V, in simple(not use formuia) how can you calculate it's HT & LT side current.
5 Answers Construction, wbsedcl,
how to calculate short circuit current for the busbar
AC SUPPLY HAVING 230 V FREQUENCY REDUCED ZERO IF MEN TACUCHES THE SUPPLY WEATHER HE GETS SHOCK OR NOT?
If I want to connect a capacitor bank on the HT side of a 11kV/415V, 3 phase delta-star distribution transformer to supply Reactive power to it..what practical specifications of a Capacitor bank that can i've??please reply..
The Source internal resitanse Rs , When equal to Load resistance RL, the maximum transfered is of _____ % of input power?
what is the Knee point Voltage?
Derive the inductance of a coil in terms of its physical factors.
how does bode plot have an advantage over root locus? how does it determine the stability of a system depending upon the location of poles and zeroes?
In Ferantti Effect Receiving end voltage is greater than sending end voltage but how it is possible. I know its all about charging current but give me some more detailed explaination?