In a panel 2500A ACB is the incoming breaker then what is
the size of the bus bar?
Answer / rsundareee
The Busbar shall be 3P+N+E =2R x 150mm x 10mm each R,Y,B,N
and Earth Busbar shall be 1R x 150mm x 10 mm.and 85kA for
breaking capacity of the Bus bar.
| Is This Answer Correct ? | 5 Yes | 1 No |
why neutral wire don't shock?
what is static excitation and dynamic excitation of synchronous generator,scr excitation is a brush or brushless excitation?
Explain with example of functional requirements of protection relay in terms reliability, selectivity, sensitivity
How to run 1ph motor(230 VOLTS its full load amps is 4.5 ampa))with 480 volts main(we didn hav neutral)Thn we go for step down transformer.Our load 10 amps,so we conisder this amps in primary are secondary side?
What is the diffrence between an ELCB(earth leakage circuit breaker) and RCCB(residual current circuit breaker)?which has higher degree of safety and why?
A 40 kva transformer has a core loss of 400W and a full load copper loss of 800W. What is The proportion of full load at maxmimum efficiency?
WHY IN WESTERN COUNTRIES THE ELECTRIC SHOCK IS VERY SLOW AS COMPARE TO INDIA.&IF ANY ONE HAVE CORRECT KNOWLEDGE THEN SEND OTHERWISE NOT
difference between the earthing,grounding and neutral
in flemings lefthand rule thumb indicate for....
why impedance test in power cables?
why name plate detail HP/KW rating of a motor is different from measured value HP/KW using formula?
what is AB switch???
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)