why surge suppressor in vaccum circuit breaker and it is
only in motor feeder why not in tranformer feeder?no surge
suppresor in ocb in motor feeder?
Answer / kalyan dilip
Surge Suppressor is used to control the current
fluctuations.In motor there will be fluctuations in current
with the change in load. So Surge Suppressor is used in motor.
In case of Transformer there will no fluctuations in current
with the change in load because voltage is maintained constant
therefore it is not neccessary to use Surge Suppressor in
Transformer Feeder.
send your feedback or your doubts to kalyan.dilip0@gmail.com
| Is This Answer Correct ? | 2 Yes | 4 No |
Calculate the demand in KVA for a three phase 440V power source drawing 1100A current
what is the similarity and difference between ups and inverter?
How can calculate the earthing strip of Copper/GI for rating of 30kV,discharge current 10KA Lightning arrester.
why DG rating in kva
why motor burns ?
what is difference between KW,KVA,KVAR? also give me the formula for all the three...
What are the advantages and disadvantages of negative feed back?
A 200 KVA UPS's load current is 70 A. We want to provide a Generator back up. What capacity of DG required for this ?
What is vacuum circuit breaker.define with cause and where be use it device?
deisel generators all elcetical calculation formule's
What is distance protection relay? where & why we use this relay?
2 Answers Siemens, UltraTech, Voltech,
what is b checks and m checks in diesel generator maintenance?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)