what is b checks and m checks in diesel generator
maintenance?
Answer / sk ajamat ali
A-Check (Daily routein Check)
1. Check oil level.
2. Check cleanliness of DG
3. Check Battery Voltage
4. Check any Leakage
5. Check all filter condition
6. Check oil Level
7. Check coolent Level
8. Check Check V-Belt condition
B-Check (Every 300- 350 Hrs.)
1. Change oil.
2. Change oil filter,fuel filter,bypass filter.
3. Change Air Filter.
4. Change water Separator
5. Radiator cleaning with chamical
C-Check (Every 800-1500 Hrs.)
1. Change oil.
2. Change oil filter,fuel filter,bypass filter.
3. Change Air Filter.
4. Change water Separator
5. Radiator cleaning with chamical
6. Check All Electrical terminal & thimbles
7. Check polution level
D-check (Every 3000- 5000 Hrs.)
1. Complete DG set should be dismental.
2. Turbo charger service
3. Injector Pin service
4. Cylinder Head service
5. PT Pump sevice &
6. Repeat same B-Check process.
If your DG set running hours more than 10,000 then in D-
Check You should need to be
1. Change Piston Bearing,
2. Change nozels,
3. Piston Cylinder also need to be change.
4. Change Canopy filter if require
5. Check polution level
Is This Answer Correct ? | 1 Yes | 0 No |
how many BUSBAR is in electrical system?
What is the function of the circuit breaker failure relay?
How we can design a cable for a 3phase load.
what is tha online tapping and offline tappchange? which side connected primary or secondary and explain ?
why T/F winding temp measurement cts are odd secondary current ie,109A/1.2A/1.4A?
0 Answers MSETCL Maharashtra State Electricity Transmission Co Ltd,
What is critical disruptive voltage?
how can service sitting be setted for MCCB?Example for sittings IR (CURRENT RATING),IS(CURRENT STARTING) I O (current operating)?
10Hp, 3-phase, 415v, 50Hz induction motor. The above motor is to run on Star-Delta connection, so how do i make following hardware selection 1) MCB, 2) Contactor, 3) Wire Gage (Depending on P-P current or Line Current), 4) OLR, Please tell in detail how to do the above, so as to get the ans. of it even if the Hp rating changes.
We have a distribution transformer of 750KVA/11kv/440v and an AVR (Servo Stabilizer) of 750KVA on the LT side of distribution transformer. Also we have an ACB of 1200A on the output of distribution transformer (that is on the input of AVR). We want to have an MCCB on the output of AVR. What should be the rating?
whatare the disadvantages occur,if the form factor of transmission will not be equal to 1.11
Give me the calculation steps to design an electromagnet to be work in 230V 50 Hz AC Supply. Also give force that is created by that electromagnet when it gets energized.
what is the advantage of pwm pulse compare to squarewave pulse.