At what distance power transformer can be placed from
generating ?
Answers were Sorted based on User's Feedback
Answer / rvg.msceb
consider a gen station producing 20MW of power at 11KV. So
current will be 1050 amps. So considering the cabling and
its loss due to heating etc, lowest distance is recommented
from gen stations.preferably less than 100 mtr.
| Is This Answer Correct ? | 8 Yes | 0 No |
Answer / rod
Any distance, the distance depend on the supply cable size
the bigger the cable the longer the distance, the higher
the voltage also determins the distance.
So the determining factor is to match the cable to the
requirements of the transformer, clearly load and volt drop
is the issue
| Is This Answer Correct ? | 4 Yes | 4 No |
Answer / hamed
Any distance and if it is close it is beter due to voltage
drop ,Ohmic losses and cost.
| Is This Answer Correct ? | 1 Yes | 2 No |
Transformer's core is made up of which material and why so?
for leading power factor penalty by SEB why
1 amp means-how many electron flow per second. ?
why transformer rating in kva ?
sir am giving jspl exam on 19th oct . i belong to eee, so plz send previous question papers ..........to dis id abhilash203@gmail.com
i wanna know that star point in transformer becomes as a neutral on secondary side now tell me that how is that possible?because if joit the all three winding ends with each other it can b short circuited.dut it doesn't.WHY?pls Answer me in brief.thanks alot
Why we are mostly using a single 3-phase transformer instead of three 1-phase transformers?
what is the conductor size in 33/11 kv line
draw the full wave and half wave circuit of 3 phase system and inverter circuit used in ups
What is different bewteen low or high impedance busbar protection scheme
I have two AC generators, the first rated 2680KVA for 380V/4345A/pf:0.7 and the second rated 3461KVA for 5500V/363A/pf:0.8. I want to parallel the two generator to a bus. The second generator passes through a transformer to down the voltage to 380V and a part of its power goes to another bus so that it's only a part of the total power of the second generator taht goes to the considered bus. I have two Basler DECS100 AVR regulator. How can I make the synchronization ? What others equipments must have ?
for star delta connection,,why the contactor star not burn,when red,yellow and blue cable is looping.
2 Answers Mahindra Water Utilities,
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)