FOR WHICH FAULTS OR CONDITIONS DOES A TRANSFORMER
DIFFERENTIAL PROTECTION DOES NOT OPERATE???
Answers were Sorted based on User's Feedback
Answer / thiru
transformer differential protection does not operate when
there is out zone fault.because that time two sides of CT's
sense same current. there is no difference of current.so
the relay does not operate.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / v.selvakumar
through fault or external fault it won't operate.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / zahid ali
Turn to turn fault it won't operate.
in other case if the neutral is grounded grounded through
high impedance or Resisted earth fault it wouldn't be
operate on ground fault.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / zahid ali
because there is no difference in the current at the ends
of a winding with shorted turn: a turn fault would have to
burn through major insulation to ground or another phase
before it could be detected
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / minu
not the ground fault, if its settings are kept low enough,
it will operate for ground fault also. i am looking for
some other answer.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / siddharth tayade
onely internal fault is detected by the diffrential relay
it will not trip under through fault condition
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / minu
no. i am asking abt the in-zone faults only. for what in-
zone faults or some conditions will it not operate.
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / minu
hi zahid, thanks for the reply. can u pl elaborate a bit on
why it wont operate on turn to turn faults or for other
cases that u mentioned.
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / minu
does that mean that a shorted turn fualt wont be detected
by any other relay too???
| Is This Answer Correct ? | 1 Yes | 2 No |
Simultaneous trip of incoming and outgoing breakers of 400kv/220kv trnasformer. What are the probable causes?
the minimum clearance b/w ceiling and plane of leaf of ceilng fan shall be ..........mm
In Megger which types of test we can do ? and How it works? How to use?
Why cannot we insulate HT over head cable to avoid ionization of air around the HT Cable?..By this we can minimise corona loss also..
When testing an earthing connection, we use a 60 or 100 candle bulb with a phase connected direct from supply and the other wire to the new earthing provided.If the bulb glows then the earth is ok.Else earth connection is not Ok. So, why dont we can use all the home appliances taking a single wire from the phase and the return connection to Earth instead of return connection to neutral?
Why celling fan rotates in anticlockwise direction and table fan in clockwise direction ? Give technical reason.
How to take the Vector Group Test in Transformer? What is the purpose of doing Vector Group Test?
Give me the calculation steps to design an electromagnet to be work in 230V 50 Hz AC Supply. Also give force that is created by that electromagnet when it gets energized.
at present how many EHVAC lines are there in India?
EHV current carrying parts need to have smooth finish,then how can a 245kv GIS with emery finish can run so long?
What is clock position of Transformer?what are the clock positions are there?and what is different of them?
Alternator couple to diesel engine why, Alternator couple to ac service motor with gear drive for 1500 rpm possible (yes or no) aim to low input power supply give to motor then high output power taken for alternator Please answer this question
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)