Answer / vinod
When two ELCB in prallel sending current & return current
of each ELCB will not be equal (example one ELCB is
sending 4 amps to the load but due parallel the retun
current from the load to the same ELCB may not be 4 amps,
retun path through other ELCB treat as a earth fault, so
one ELCB will trip.
| Is This Answer Correct ? | 8 Yes | 0 No |
Answer / karthick
pls to be check elcb current rating in case rating are
different. lower rating elcb got easily tripped. in case
elcb rating are same connecting load to be check
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / prashant
if loae is high then you connect two cb, if any one of cb
is trip then ohter cb is also trip. Due to high current.
because if any cb is trip then all current is flow through
the second cb.
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / arvind
when you are connecting two ELCB parallel then its mean the
voltage between these will be same but not the current, so
which ever ELCB is connected to higher current side is
getting trip if the current is flowing greater than the set
value.
| Is This Answer Correct ? | 4 Yes | 4 No |
Answer / purushotham
the ELCB's are connected in parllel, so the voltage in the
ckt is equal but current is diff. so if one coil trips the
ckt will works on second ELCB and total loading depends on
that second ELCB.
| Is This Answer Correct ? | 0 Yes | 0 No |
What is CVT and what is relation with wave trap?
What is the permissible limit of shaft voltage for 6.6 KV motors ? Why? Is there any standard is available?
What is principal to reduce earth leakage current with isolation transformer? When isolation transformer is installed in input stage of system, earth leakage current is reduced. the reason is why the leakage current of 2nd stage of isolation transformer does not affect the 1st stage's leakage current. I would like to know the reason. As you know, earth leakage current is a kind of AC. So, How to reduce earth leakage current in case that isolation transformer is used?
Megger type of instrument is used to check??
What is dry and wet flashover.
what is the principle of dc generators?
what is ratio of copper wire size and current ?
how do i get electrical supervisor certificate in gujrat?
3 Answers DGVCL Dakshin Gujarat Vij Company, Infosys, ONGC, Orient, Reliance,
I am getting above 60 V as open delta voltage against single phase unit ICT at tertiary delta formed and ICT getting trippped on NDR. ICT tested and found in order. PTs provided on tertiary are tested and in order. what may be the reason?
what heppend if we are connected u1-v1-w1 as a star point in the place of u2-v2-w2 in power genration
single phase voltage 230 and Three phase voltage 450 why 690 voltage
If a line which is drawing approximatly 2100amps what should be earthing streep size(using galwanize streep)?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)