WHEN I AM CONNECTIN TWO ELCB IN PARALLEL.ONE ELCB
TRIPPED...HOW IT HAPPEND??
Answers were Sorted based on User's Feedback
Answer / vinod
When two ELCB in prallel sending current & return current
of each ELCB will not be equal (example one ELCB is
sending 4 amps to the load but due parallel the retun
current from the load to the same ELCB may not be 4 amps,
retun path through other ELCB treat as a earth fault, so
one ELCB will trip.
| Is This Answer Correct ? | 8 Yes | 0 No |
Answer / karthick
pls to be check elcb current rating in case rating are
different. lower rating elcb got easily tripped. in case
elcb rating are same connecting load to be check
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / prashant
if loae is high then you connect two cb, if any one of cb
is trip then ohter cb is also trip. Due to high current.
because if any cb is trip then all current is flow through
the second cb.
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / arvind
when you are connecting two ELCB parallel then its mean the
voltage between these will be same but not the current, so
which ever ELCB is connected to higher current side is
getting trip if the current is flowing greater than the set
value.
| Is This Answer Correct ? | 4 Yes | 4 No |
Answer / purushotham
the ELCB's are connected in parllel, so the voltage in the
ckt is equal but current is diff. so if one coil trips the
ckt will works on second ELCB and total loading depends on
that second ELCB.
| Is This Answer Correct ? | 0 Yes | 0 No |
i seen a 132kv/11kv transformer,and thier is a sugar factorys 10MW EXPORT PLANT,MY QUESTION IS THAT WHEN THEY EXPORT ELECTRICITY THEY USE THE SAME TRANSFORMER AND THE CONNECT IT TO 132/11KV TRANSFORMERS SECONDARY SIDE CAN ANY ONE EXPLAIN IT.. THE TRANSFORMER IS OF KIRLOSKAR MAKE AND IT HAS TAP CHANGER.
generally the electrical equipments not to be operated at leading power factor, why?
what is active power & reactive power?
whenever any squirrel or a crow falls on the transformer input line then there is a big explosion and 440 volts of power is being discharged through the neutral line due to which appliances in off mode are also burned.we have earthing for the transformer as well as the bus bar chamber.why is it happening?
why we use 630mm single core cable for transformer secondary side and why two neutral cable
what is the formula for transformer oil?
Transformer not operated in dc ! why?
Shall I use 40A semiconductor Fuses in 32 A SFU ? Frame size is same. What Happen if Fuses burn on SFU?
What is 2P*0.5 sqmm screened copper cable and what is the use of it..?
Does the direction of rotation of d.c. Shunt motor would get reversed if the armature current and field current both are reversed?
Hello friends., my question is related to testing of current transformer... A Ct having knee point voltage of 750 volts., and I have two step up transformer's of rating 230 v to 440 volts., can I obtain the value of 750 volts by using the two transformer's.... If yes then how could I connect the transformer's to obtain knee point voltage?? thank you in advance
how we calculate the motor rating of pump for water suction ?its any formula for that plz give thank u
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)