what are protective device needed to power a
360W ,50hz,240v,single phase,0.65 pf universal motor
Answer / suresh natarajan
Active Power: 360 Watts
Apparent Power:360/0.65=554 VA
Load Current 554/240=2.31 Amps
Protection Device should be 3-5 Amps.
Is This Answer Correct ? | 14 Yes | 1 No |
formula for cable size calculation for current?
10 Answers KL Power, ONGC, RL Clean Power Pvt Ltd RLCPPL, SAS, Sobha Developers,
what is synchronizing panel & its working.
what happen when ac motor is connected with dc current
We are using Powerica make 100 KVA DG set. Whenever i connect compressor on DG load (Compressor Make Atlas Copco 5.5 kva) that time we face the lot of fluctuation on Dg output. Can you please suggest me how can prevent this fluctuation?
What is the use of Exciter in generator? & what will be the current of Exciter in 500 KVA DG Set?
what is the meaning of DY-11 Z-5%
Why should we use the igniter in the sodium vapour lamp.
7 Answers ABB, Delphi, Mudhra, NTPC, PICT,
Explain why the Voltage drop will happen in 3 Phase line?
Why RCD trips on connecting to one Socket but not trips one other circuit on same RCD.
what work will do diffrential realay DG set
0 Answers IG Petrochemicals Ltd,
what is p.s impedance measurement test in earthing transformer?
what is motor capacity of 80TR chiller? and also say what is the formula related temperature, motor capacity, TR?
0 Answers Apotex, Periyar Chemicals,