what are protective device needed to power a
360W ,50hz,240v,single phase,0.65 pf universal motor
Answer / suresh natarajan
Active Power: 360 Watts
Apparent Power:360/0.65=554 VA
Load Current 554/240=2.31 Amps
Protection Device should be 3-5 Amps.
| Is This Answer Correct ? | 14 Yes | 1 No |
What are the uses of MCB & ELCB ?
which relay is used on long transmission lines
10 Answers ABB, Bhel, Student, Tata Steel Limited,
1.wat is the negative slip region in the motor?
What is the operating range(tolerance) of voltage and frequency of grid supply in india?
why the Parameters : Base Voltage & Maximum Voltage can't be equal in value in a VFD (Variable Frequency Drive) ? How much the base voltage would be lower than the maximum voltage ? If 400 V is the 3 phase output of a VFD ... then what should be the base voltage ? thanks a lot
Where double earthing is required? Is there any power specification to have double earthing?
Which of the following loss varies with the load A hystresis loss B eddy current loss C copper loss D core loss
In all electric motors, fans are provided to dissipate heat. How it dissipate the heat? By absorbing atmospheric air or by exhausting the heated air generated while running?
WHERE IS THE LIGHTING ARRESTER SHOULD BE PLACED IN DISTRIBUTION LINES?
why we are using earth pit in sub stations.?
What is the different between earthing & Neutal
how a single machine can act as both motor and generator? and give explanation interms of connections?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)