how to measure the voltage drop in cables also give
formulas to calculate.
Answers were Sorted based on User's Feedback
Answer / ajay daultani
Voltage drop ( % ) =1.732*I * L* (( R *(cosfie) + X*sin
(fie ))* 100 /( n*v*1000)
where I is load current
L is length of cable
R - resistance
X - reactance
fie is angle calculated by tan^-1 ( R/Z )
n is number of runs
v is voltage
| Is This Answer Correct ? | 16 Yes | 6 No |
Answer / nagaraju .n
In an cable resistance is depending on
length ,crossectional area, tempreture,
find the specific resistance of the cable:R=RWO*A/L.
THAN FIND THE VOLTAGE DROP .
| Is This Answer Correct ? | 7 Yes | 6 No |
Answer / ashish
Voltage Drop For Different Type of Cable Is As Specified By
The Cable Manufacturer In Terms Of Volt/Amp/Length(meter)
so with the Help of that We can Calculate The Voltage Drop
Practically At Most 10% Voltage Will Be allowed
| Is This Answer Correct ? | 6 Yes | 10 No |
What is your favorite aspect of the engineering field?
Magnetizing current for induction motor compared to transformer is= A equal B more C less D depends on load
In cable sizing calculation (determining the max route length of cable) why we choose the shortest length between cable length of full load current Iflc & starting current Istart?
what does vector group Dyn11 tell us? also tell me how will u differentiate between phase lead and phase lag thru this vector group
Sir if i have 2kv ups in which 17ah 8 battries load 600watts how much back up time i get and if i put 6kv ups with the same no of battries same amp can i get more back up time please give reply exactly what is the procedure to calculate back up time for different kv,s
what would happen when synchronous motor will operate beyond syncronous speed?
how much Amp we can put in 1200kva generator?
what is the necessary of using inductance property in transmission lines even through resistance is used to opposes the high current flows in that?????
Difference between transition and diffusion capacitance
what happens when parallel resonance occurs?
How to measure power in 2 or 4 or n phase circuit? Please give me a formula.
How much pole motor can be desion for 415 volt ,50 hz.Power supply. in pratical condition . Prakash veer singh
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)