New istallation how many eathing have one transformer?
Names of earthing connect places?
Answers were Sorted based on User's Feedback
Answer / makpsingh
Any transformer should have atleat four earthings.
2 connections for its neutral earthing and
2 connections for its body earhtings
All the connections should be with dedicated earth pits
which may be interconnected for relaiblity and to have
lower earth reistance value.
These earth pits should be duly marked and to be tested on
a dry day once in year of earth reisistance and earth
continuity. Earth Resistance value should be less than 5
ohms and if it is greater then these earth pits should be
treated to bring dowun the value.
| Is This Answer Correct ? | 61 Yes | 4 No |
Answer / vijay sagar reddy
Any electrical parameters have 2 Earthins
: 2 Neutral Earthing
: 2 Body Earthing
| Is This Answer Correct ? | 30 Yes | 0 No |
Answer / vijay sagar reddy
Any electrical parameters have 4 Earthins
: 2 Neutral Earthing
: 2 Body Earthing
| Is This Answer Correct ? | 15 Yes | 6 No |
Answer / gaurav sinha
Any transformer should have atleat four earthings.
2 neutral earthing and
2 body earhtings
| Is This Answer Correct ? | 9 Yes | 1 No |
Answer / manikandan
Thats depends upon the vector group of the transformer.in
case star-star,the neutral earthing is require 4Nos
(Primary/Secondary)earthing and transformer body is
required 2Nos earthing.Types of earting is more than 2.That
is depends upon the standard practice.
Types
1.Direct earthing(In India)
2.Inductance earthing(In practice in UN)
3.Using resonant coil
| Is This Answer Correct ? | 3 Yes | 2 No |
Answer / kishore
along with above said earthing thransformer bushing is also
earthed which is mandatory
| Is This Answer Correct ? | 8 Yes | 8 No |
Answer / hero
along with above said earthing thransformer plate earthing
is required
| Is This Answer Correct ? | 5 Yes | 5 No |
Answer / ravi nalli
Whether neutral (from neutral bushing) is connected tank
body is correct
| Is This Answer Correct ? | 2 Yes | 3 No |
Answer / manikandan
Now days in normal practice we are using 100mm Dia cast
iron pipe length of 2.5Mtr.It is good conductivity compare
the pipe and plate earthing.
| Is This Answer Correct ? | 0 Yes | 8 No |
how wecalculate breaking capcity of acb mcb mccb .explain with example
What is the ideal position cooling fan inside the dc motor?
What do you mean by phasors?
how many earthing required for ups, what should be the earth voltages
what is DAR test?
2 Answers Al-Naboodah, ISRO, ONGC,
what is compatible kva for 3300 watts and why
what type of loads are inductive load & resistive load ?how they different between each other ?
why we do not switched on capicitor panel with DG Supply
what is the meaning and difference between ELECTRICAL DRAWOUT and MANUAL DRAWOUT?
how vfd drives energy save
Where I can get the sample question for post of Junior engineer electrical-II For RRB Bhubaneswar.
what is the power factor
13 Answers Heidelberge Cement,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)