New istallation how many eathing have one transformer?
Names of earthing connect places?
Answers were Sorted based on User's Feedback
Answer / makpsingh
Any transformer should have atleat four earthings.
2 connections for its neutral earthing and
2 connections for its body earhtings
All the connections should be with dedicated earth pits
which may be interconnected for relaiblity and to have
lower earth reistance value.
These earth pits should be duly marked and to be tested on
a dry day once in year of earth reisistance and earth
continuity. Earth Resistance value should be less than 5
ohms and if it is greater then these earth pits should be
treated to bring dowun the value.
| Is This Answer Correct ? | 61 Yes | 4 No |
Answer / vijay sagar reddy
Any electrical parameters have 2 Earthins
: 2 Neutral Earthing
: 2 Body Earthing
| Is This Answer Correct ? | 30 Yes | 0 No |
Answer / vijay sagar reddy
Any electrical parameters have 4 Earthins
: 2 Neutral Earthing
: 2 Body Earthing
| Is This Answer Correct ? | 15 Yes | 6 No |
Answer / gaurav sinha
Any transformer should have atleat four earthings.
2 neutral earthing and
2 body earhtings
| Is This Answer Correct ? | 9 Yes | 1 No |
Answer / manikandan
Thats depends upon the vector group of the transformer.in
case star-star,the neutral earthing is require 4Nos
(Primary/Secondary)earthing and transformer body is
required 2Nos earthing.Types of earting is more than 2.That
is depends upon the standard practice.
Types
1.Direct earthing(In India)
2.Inductance earthing(In practice in UN)
3.Using resonant coil
| Is This Answer Correct ? | 3 Yes | 2 No |
Answer / kishore
along with above said earthing thransformer bushing is also
earthed which is mandatory
| Is This Answer Correct ? | 8 Yes | 8 No |
Answer / hero
along with above said earthing thransformer plate earthing
is required
| Is This Answer Correct ? | 5 Yes | 5 No |
Answer / ravi nalli
Whether neutral (from neutral bushing) is connected tank
body is correct
| Is This Answer Correct ? | 2 Yes | 3 No |
Answer / manikandan
Now days in normal practice we are using 100mm Dia cast
iron pipe length of 2.5Mtr.It is good conductivity compare
the pipe and plate earthing.
| Is This Answer Correct ? | 0 Yes | 8 No |
I am selected in OCL(Orissa cement Limited), but they have a Tech PI round their at their plant.Anybody has any idea that what kind of questions they are going to ask??Please guies help me. I am in serious headache.I have heard that huge elimination is done at there.
what is the diffrence between kav and kvar?
why transformers are rated in KVA
Transformers with dc supply
Which one is given high energy in same power consumption AC or DC
As we know that during saturation test of CT from secondary side, the current in secondary shoots up after core saturation. How core saturation effects the secondary current?
Dear sir, my knowledge about cable size determination is limited. Though I read examples I could not calculate the Cable size required for electric driven pump 40 KW, 380 Volt, 50 HZ, 50 meter from transformer and it is three phase star delta starting. Please help as there is no one in my surroundings to help.
if three phase supply is given to single phase transformer, what will happen?
Can i connect all earth pits in ring system..., And wat IS 3043 says...please help me
How silicon gel sucks moisture in the transformer, its have any small exaust fan behind silicon gel.
what is the meaning of impedance protected in instrument cooling fan
what is IP55,IP65
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)