in 50 mw generator if field is open in full load running
condition what happen and for protection which relay used?
Answers were Sorted based on User's Feedback
Usually we are using a loss of excitation rely. Which
always getting a sense from the field excitation circuit
continueslly during the runing condition of Generator.
Is This Answer Correct ? | 9 Yes | 0 No |
Answer / a1
I is depend on type of operation-
1) If parrallel with grid/Other generator, than it will
draw reactive power from the Grid/Generator and give active
power to the load. It will work as a Induction Generator.
Reactive power of connected circuit will unbalance.
2) If Generator is running island mode(without any other
source), than terminal voltage of genertor will start to
decrease and current will start to increase. Winding temp.
of Generator and drives will increase.
Under excitation relay provide for this.
Is This Answer Correct ? | 4 Yes | 1 No |
Answer / deepak
it run as induction gen & draw excitation power from grid
Is This Answer Correct ? | 5 Yes | 3 No |
Answer / prodip das
It acts as a load, Sensing relay of excitation voltage
Is This Answer Correct ? | 0 Yes | 2 No |
What is the difference between ELCB and RCD
In response to Mr Bikas. If fault current is 52 kA then what will be the CT specification
how to calculate units consumption for a 12 hp motor /hr.
A 3 phase transformer's (Y-Y) Y and B phase is (Y and B connection not broken) broken from neutral and R and Nutral connection is ok, what will be the relay tripping and why
how calculate busbar size for rated amps, which formula use
30 kVA and voltage 380/220VAC how to find out kA?
When we use air circuit breaker, it has O/L protection ,time delay SC protection, Instataneous SC protection & ground fault protection. They all have some setting range. But what is the suitable/allowable setting for the above protection which will be safe for the equipment? For example-O/L protection setting have a range of (0.4,0.45,0.5,0.55,0.6,0.65,0.7,0.8,0.9,1.0)xIn Time delay SC protection have a range of (1.25,1.5,2,3,4,6,8,10,12)xIn Time delay setting is 0.02,0.1,0.2,0.3,0.4 Instataneous setting is fixed to 20xIn Gound fault setting is given 100A,300A,600A,900A,1200A This setting are for 2500A ACB. So what will be the basic allowable setting for the above protection? is there any formulae to calculate this<
What will happen if the armature resistance is in minimum position and the field resistance is in maximum position while starting the motor
how to calculate the battery AH
what is the all safty name of diesel genrator?
what is the effect when the shunt field winding is opened in dc shunt motor (i) at the time of starting ? (ii) in running condition ?
exolain the star delta connection