WHAT HAPPEN IF LT SUPPLY 415 V FED TO THE HT 3.3KV MOTOR
please note that insulation of the motor is rated for
3.3kv.,which is a medium voltage.
Now ,when we apply a low voltage 415v, the motor will crawl
and draws heavy current.so the upstream device or the
circuit breaker trips.
We have also experienced that cubile arcing fault takes
places and burns the cabinet metal clad cabinets.If it a
old module,then the arc chute of the CB FEEDER burns/smokes.
| Is This Answer Correct ? | 0 Yes | 5 No |
Name two types of electrical analogous for mechanical system.
what is voltage rise and voltage drop?
Transformer Secondary maximum current (max. load)
what is the rating of power generation in india?
Why semi-conducting insulation is used in XLPE cables?
how to make a solar panel? why solar panel cell connected to serious?
Hello Friends, How can we recognize the CT Star Point is S1 or S2 in case of Electro Mechanical Relays and what is meant by Restraining coil in relays and what is the purpose of that.. thank you in advance..
what is the safety points of vaccum circuit breaker.
What are the types of the glands and difference between single and double compression type of cable Glands.
0 Answers ABC, All Trades Electrical,
11. As per the theory current doesn’t flows in Neutral, but practically it is not applicable, explain why? 12. How to take the Vector Group Test in Transformer? What is the purpose of doing Vector Group Test? 13. Why the transmission lines are in 11kV, 22kV, 33kv, and why not 10kV, 20kV, 30kV? 14. Why do we generate 3 Phase AC Supply? It is possible to generate 4 Phase and 5 Phase explain it? 15. Explain why the Voltage drop will happen in 3 Phase line? 16. What is the equipment used to control the generator output? 17. What are the factors to be considered during the Synchronization? 18. What should be value of Circuit breaker operating time and tripping time? 19. Why the CT Secondary is rated as 5A generally? 20. At which time Synchronous generator act as a Synchronous Condenser?
show the physical connection and phasor diagrams of 1: DZO 2: Yd1 3: DZ6 4: Yd11 5: YZ11
why should the primary of transformer be connected in delta in a heat run test?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)