how can you calculate the value of external resistance
inserted in a slipring industion motor? (eg. 110 kw / 990
rpm/50Hz/stator v-415/stator Amp-195/Rotor V-440/Rotor amps-
151.)
Answers were Sorted based on User's Feedback
Answer / rakesh patel
Formula: K=
R.V/1.73R.A
where R.V=Rotor
voltage ,
R.A=Rotor
Current ,
K=constant ,
than
1step=1.40K ,
2step=.35K ,
3step=.15K ,
4step=.08K now
put the data and
get your ans.
| Is This Answer Correct ? | 88 Yes | 34 No |
This motor is used for both purpose as it is used in 15 Ton
EOT crane main Hoisting / Lowering application. External
resistance used for speed control & for High Starting Torque
both.
| Is This Answer Correct ? | 23 Yes | 5 No |
Answer / p.veerapandian
Can u tell the application of the inserting external
resistance in the rotor circuit for speed variation or
starting with heavy torque application
| Is This Answer Correct ? | 23 Yes | 6 No |
Answer / prashant
All hoist and travel drives in EOT cranes, or any equipment for that matter, that use Slip Ring Induction Motors and need speed variation use these resistance boxes. The method of calculating steps in external resistance is absolutely correct as told in 1st answer.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / gulzar ahmad naikoo
There is thumb Rule for percentage of cutting resistance.1st step full calculated resistance,2nd 50% of total,3rd,50% of 2nd,4rh 50% of 3rd, and so on.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / prakash gidde
Mr. Rakesh, Pl explain how many % of external resistance need to cut en each step during operation of slip sing motor? also pl explain on which bases u considered 1.4, 0.35, 0.15 & .08 value for calculation of step wise resistance.
cutting of resistance should be on application of motor where to we are going to use & lifting load capacity. Also its depend on which type of resistance we are using -- SS punch plate grid / punch wire grid/ oil merge/ liquid water resistance.
| Is This Answer Correct ? | 0 Yes | 2 No |
What will be the resultant out put voltage when two different voltage rating batteries are vconnected in parallel? pls. answer with example if available.
What is the difference between UPS & inverter ? which UPS is better and whos got the edge ? what is the difference between & inverter ? which UPS is better and whos got the edge 12 V , 24 V , 36 V etc what are the advantages of 12 V, 24 V , 36 V etc and what are the disadvantages of 12 V, 24 V, 36 V etc thanks
1)which height building required lightning arrester? 2)how to calculate the requirement of lightning arrester? 3)what is the pro instrument? 5)how to test protective relay like overload?earth fault relay?
Why 36 KV LA is used in 33 KV Line and 9 KV LA is Used in 11 KV Line
1 Answers APTransco, Bhel, Wipro,
WHAT IS THE ANALYSIS OF FREE WHEELING DIODE IN FULL WAVE CONROL RECTIFIER?
What is Meter MF if External CT Ratio is 150/1 , PT Ratio is 132/110 Meter CT Ratio is 200/1 & Meter PT Ratio is 110/1
what is residual current....
what is phase angle ? and also tells me why my phase-phase voltages are 390 rather then my single phase voltages are 221 and 223 respectivly?
2.5mva transformer is installed in our company with oltc but it is not working in auto mode ,it is operative in manual mode control wiring is done how can i rectify it?
why we are using earth pit in sub stations.?
how many number of terminals are available in CURRENT TRANSFORMER
6 Answers MSETCL Maharashtra State Electricity Transmission Co Ltd,
how can i design a APFCR panel? please explain with example..
1 Answers Milestone, Reliance Jio,
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)