how can you calculate the value of external resistance
inserted in a slipring industion motor? (eg. 110 kw / 990
rpm/50Hz/stator v-415/stator Amp-195/Rotor V-440/Rotor amps-
151.)
Answers were Sorted based on User's Feedback
Answer / rakesh patel
Formula: K=
R.V/1.73R.A
where R.V=Rotor
voltage ,
R.A=Rotor
Current ,
K=constant ,
than
1step=1.40K ,
2step=.35K ,
3step=.15K ,
4step=.08K now
put the data and
get your ans.
| Is This Answer Correct ? | 88 Yes | 34 No |
This motor is used for both purpose as it is used in 15 Ton
EOT crane main Hoisting / Lowering application. External
resistance used for speed control & for High Starting Torque
both.
| Is This Answer Correct ? | 23 Yes | 5 No |
Answer / p.veerapandian
Can u tell the application of the inserting external
resistance in the rotor circuit for speed variation or
starting with heavy torque application
| Is This Answer Correct ? | 23 Yes | 6 No |
Answer / prashant
All hoist and travel drives in EOT cranes, or any equipment for that matter, that use Slip Ring Induction Motors and need speed variation use these resistance boxes. The method of calculating steps in external resistance is absolutely correct as told in 1st answer.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / gulzar ahmad naikoo
There is thumb Rule for percentage of cutting resistance.1st step full calculated resistance,2nd 50% of total,3rd,50% of 2nd,4rh 50% of 3rd, and so on.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / prakash gidde
Mr. Rakesh, Pl explain how many % of external resistance need to cut en each step during operation of slip sing motor? also pl explain on which bases u considered 1.4, 0.35, 0.15 & .08 value for calculation of step wise resistance.
cutting of resistance should be on application of motor where to we are going to use & lifting load capacity. Also its depend on which type of resistance we are using -- SS punch plate grid / punch wire grid/ oil merge/ liquid water resistance.
| Is This Answer Correct ? | 0 Yes | 2 No |
what is motor
why we are using auto transformer in sub station mostly???
22kV HT incoming should be 3 phase or 4 phase? why is it not 4 phase?
what is a synchronizing lamp ?
what is principle of DC machines?
5 Answers APTransco, NTPC, Wipro,
area control error
how the fan is switched off immediately switching off the switch?
What is MS-EXCELL?
How to take the Vector Group Test in Transformer? What is the purpose of doing Vector Group Test?
While testing the 33KV Busbar by using Hipot kit, what should be the test voltage we have to apply
number of I/O devices in siemense plc
can anyone explain 11kV 3core cable megger,hi pot test procedure with connection details?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)