WHAT SHOULD BE THE RATING OF generator required to run a
pump motor of 45 Kw.
Answer / sachin kusumkar
KW = KVA*PF,
45KW = KVA*0.8
KVA = 56.25
Considering DG Efficiency 80% of rated KVA=56.25*1.25=70
cONSIDERING 20% SPARE /FUTURE LOAD KVA=70*1.2=84
so you need to select nearby available rating for selected brand in the market.
| Is This Answer Correct ? | 11 Yes | 1 No |
what is the major difference between LIBBP & HIBBP.. which one is most preferable..
what is the accaptable voltage between neutral to earth & How to reduse the resistance of earth in chemical earthing
Why current Transformer is rated by 100A/5A/5A?
can u give me a brief idea about power line carrier communication ??
What is the significance of %Z in case of transformer?
what is high voltage in india?
1kva=how many kw & amps
What type of a DC motor would you use for a lift?
how to calculate capacitor rating for an induction transformer ex.for 12 mva furnace calculate capacitor rating
where connected OLTC for transformers?
HOW DO WE COLLECT THE SOLAR ENERGY AND DESCRIBE THE METHODS TO CONVERT THE SOLAR ENERGY INTO ELECTRICAL ENERGY?
if power factor comes in leading & showing -0.95. Is there any effect on electrical system? if yes, then please tell me what would be the effects. & how long we keep power factor in leading. Keeping power factor in leading shows more KW & less KVA is it correct or not.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)