Differential Protection:
1. It simultaneously compares the phaser difference & magnitude of the current entering & leaving the protected zone.
2. It works on kirchoff's current law
3. It is a unit protection scheme i.e. it needs current inputs from minimum two different sources.
4. Differential current = |I1+I2| --> Vector sum
5. It cannot be used to provide backup to other relays
6. %Slope = (Id2-Id1)/(Ib2-Ib1)
Distance Protection:
1. It calculates the apparent impedance of a line with the help of voltage & current input connected to the relay. If measured impedance falls below set impedance trip command is issued to clear the fault.
2. It works on impedance measuring principle
3. It is a non-unit protection but can be easily used as an unit protection by co-ordinating distance protection with PLCC
4. Z=V/I
5. It can be set to provide backup to adjoining lines & bus bar depending on the requirement.
| Is This Answer Correct ? | 30 Yes | 0 No |
Post New Answer View All Answers
in dc shunt motor if field winding is shorted then
How will change the frequency in distribution side?
hey guys help me out.....what are the industrial uses/functions of nozzles in industries
which is the most advanced form of SF6 BREAKER?Can we use other gases to quench the arc?
how does a shunt reactor maintains the bus voltage???
How can we increase the capacity of Energy.?
We are planning to synchronized DG's with our captive plant in the event of black start of plant, but before sync we checked voltage of DG with our plant voltage and it varies from 5 V to 450 V. So in this condition how we can sync DG with plant ?
Discuss about gear cutting machines.
What is the maximum number of swithes that can be connected in series up to down stream point in an LV Distribution system?
While performing stability test of differintial cts how to know the voltage and current on both side of the transformer?
What is the formula to find out two phase active & reactive power
How much current will a 5 HP delta connected motor at no load will take?Is tat need a starter
What is the name of the winding from which the supply is taken for load connections?
what is the ground fault relay,which purpose it will be use,clearly tell me plz
what is mind in cable