Is a DC Transformer Possible? if Yes, Then Why, if not Then Why?
Answers were Sorted based on User's Feedback
Answer / prabhakaran
DC transformer is not possible.according to transformers
mutual induction principle,which can possible only on
alternating current (AC).
Is This Answer Correct ? | 18 Yes | 2 No |
Answer / uttam kumar sarkar
It's Impossible, because DC cannot produce Mutual Flux.
Is This Answer Correct ? | 15 Yes | 1 No |
Answer / suresh kumar k
The question itself is a little wrong, infact the question
should be "Why we will not apply DC to a Transformer, if it
applies what happens?
The answer is, there is no inductance effect produced in DC
as such in AC. If we apply a DC voltage to the primary of
the winding then there will be no Back EMF produced in the
primary winding because of lack of self inductance in the
winding for DC. Hence huge currents of the order of
thosands of Amps flow in the Pri. winding and leads to fire
in the winding. Also Since there is no mutual inductance
effect in secondary of the winding there will be no induced
EMF in secondary.
Is This Answer Correct ? | 9 Yes | 0 No |
Answer / animesh verma
DC transformer is possiblle...
Its a well known topic of HVDC area..
See any HVDC book and look for DC current transformer it is
used to sense the current in HVDC links it has got two
rings over a straight rod and has got some AC bias...
Is This Answer Correct ? | 3 Yes | 2 No |
Answer / kakanivenkatesh
transformer works in mutual inductance principle ..mutual
inductance is possible only for ac..
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / ashish verma
no it is not possible bcz there is constant flux
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / naresh
it is possible for small applications.the ransformer will
work for small period of time for given DC input as it will
produce little amount of flux for some time, but not
constant.as the flux is not constant, we prefer AC
transformer.
Is This Answer Correct ? | 1 Yes | 3 No |
11KW Delta motor is taking about 44Amps in star and goes upto 70Amps in delta and trips OFF. The rated current is 26Amps. Application is for the blower. The motor takes ( no load without coupling impller ) only 2.5A and 5Amps in star & delta starter test.Need to know why its taking high current.
During Load testing of battery charger with temporary AC Generator .When reach 70% load Generator immediately shutdown .we could not able to Recognize ,what is exactly problem .Please kindly clarify us
Why the stator is rotated in ceiling fans not Rator?
how to select the isolation tranformer for siemens 802dsl cnotroller
Why oil preferred over the air as a cooling medium for high rated transformer?
How Calculat the Cable Sizing of HT/LT System & Explian by one Exampal?
Where double earthing is required? Is there any power specification to have double earthing?
75 kw motor take 45 amp in no load delta in star 10 amp but in load it will take 160 amp but IR velue of winding above 500 at 1kw ph to earth and ph to ph. what problem it should be?
What is the relay function?
what is conductor constant taken for calculation of voltage regulation of 11 kv and 33kv line on dog aor rabbit conductor
1 Answers CSPDCL-Chhattisgarh State Power Distribution Company Limited,
how we have to calculate the short circuit current for 33/11kv 2mva, 7.5% Z, Transformer primary side breaker and secondary side breaker short circuit current for both sides?.
What is the difference between AVR and Servo Stabliser