Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


why transformers are rated in KVA

Answers were Sorted based on User's Feedback



why transformers are rated in KVA..

Answer / aslam ali

Transformers has two types of losses i.e. Load loss/copper loss & iron loss/no load loss.Load loss mainly depends on cureent(I)& no load loss depends on voltage.As a transformer never generate power,it only transfer VA or burden or load.So it's rating is always called in terms of VA.

Is This Answer Correct ?    8 Yes 0 No

why transformers are rated in KVA..

Answer / guest

iron loss depends upon voltage and copper loss depends upon
the curent.so the product of those are the power.thats why the
transformers are rated in VA or KVA.

Is This Answer Correct ?    6 Yes 1 No

why transformers are rated in KVA..

Answer / sunil kumar sinha

Transformer is an electrical device which transform power
from one voltage level to another voltage level. i.e
promary to seceondrt voltage level. It may be step up , may
be step down.
The transformer design is limited by two parameters : 1)
Voltage 2) current.

Voltage parameter decides the amount of insulation over the
coil/ windings to prevent interturn fault or earth fault of
transformer windings.Hence predetermined voltage level of
primary and secondary will decide the amount and nature of
winding insulation.
The second parameter is current which is responsible for
generating heat in the winding thus the transformer. If
transformer current is increased the heat loss will
increase and further heat transformer. The temperature of
transformer winding is controlled by cooling deviec of
transformer which is also predetermined and can restrict
winding temperature within its limit for a defined rise in
temperature. we all are well aware that rise in winding
temperature beyond given limit weekens the insulation and
results in failure of insulation, hence transformer.
due to above two reasons we must define the voltage level
and the current level of transformer. the product of these
two paramenter is VA or KVA, hence transformer is to be
rated with KVA.Power factor plays no role to limit the
transformer function, hence it is not rated in terme of
power.

Is This Answer Correct ?    1 Yes 1 No

Post New Answer

More Electrical Engineering Interview Questions

How to know the back up time for a 5KVA UPS which is connected to 15 nos. of computers? Is there any formula for this? pls. tell me.

1 Answers   S V Sugar,


in 50 mw generator if field is open in full load running condition what happen and for protection which relay used?

5 Answers   century,


How we do the maintenance of Servo motor, even we cant open it?

0 Answers   ITC Infotech,


How to calculate approximate load loss of a distribution transformer by knowing %ge imp of transformer?

0 Answers  


why we use star and delta connection?why we donot give the supply directly?

12 Answers   Hitech, Siemens, Tata Steel Limited,


wats the procedure to calculate no of batteries for ups?

1 Answers  


how to calculate the settings for shaft ct protn in hydro generators

0 Answers  


What is the difference between AC Drives and DC Drives?

14 Answers   College School Exams Tests, La-Gajjar Machineries, LG, Schneider, SMEL,


explain why reduced voltage starters are required for large tree phase inudction motor

2 Answers  


what is difference between delta-delta,delta-star transformers ???

3 Answers  


Is your generator is automated or manual if so do you know the circuits?

7 Answers   RRB,


What are the usege & different between UPS & batteries with charging system in in Substation?( UPS 120V AC & battery charger is 120v DC)

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)