In industries Power factor is maintained by installing a
suitable KVAR bank, How is the PF maintained for domestic
use, where is the capacitor bank connected
Answers were Sorted based on User's Feedback
Answer / bijay
For domestic supply ( 1 Phase) the PF variation is
comparatively low.
It is maintained at 0.95 by the Supply authority
(electricity board).
Capacitor Bank is located at the main
receiving/Distribution Station.
Is This Answer Correct ? | 18 Yes | 1 No |
Answer / raj
MAIN THING THE PF IS MAINTAIN FOR INDUCTIVE LOADS . IN
DOMESTIC WE HAVING THE RESISTIVE LOADS . BUT IN WE USING
FAN MOTORS AND SINGLE PHASE MOTORS ETC WE KNOW IN EVERY
SINGLE PHASE MOTOR WE CONNECT THE CAPACITOR IN SERIES OR
PARELLEL.SO PF IS MAINTAINING.
Is This Answer Correct ? | 8 Yes | 4 No |
Answer / rahul
we provided capacitor banks in the substations and
monitoring the variations in the load for all areas were
the loads distributed its done by with the help of aload
dispathing center
Is This Answer Correct ? | 2 Yes | 3 No |
describe the Tranformer testing procedure
what does kirlosker deals with?
Why Generator KVA not in KW ?
3 Answers Bygging India, HHH, Tata Motors, TVS,
what is closing resistor in circuit breaker? why it used?
why 3 phase motors are preferable over single phase motors ?
Hi.I want to ask how to calculate contactor rating current? for example I have 460 V , 100 A (induction motor) calculate contactor rating current?
our company have 750 kva oil transformer.still we have facing a problem that is when voltage is 11.5 kv coming from HT side then LT-side voltage is 420v or above at tape 1.please give me best solution to decrease the voltage.
explain the working principal of the circuit breaker?
We have two Al.busbars each of size 125mm*10 mm connected in parallel.To increase the current rating ,can we connect third busbar of size 100mm*10mm in parallel to existing two busbars?In my opinion ,if we connect busbars of different sizes in parallel,then the busbar of lowest size will take much current.So this type of paralleling should be avoided .Am I correct?
what is the difference betn earthed and unearthed cables which is commanly used why?
what is the minimum winding resistance of 30hp compressor, to run or to switch on
How you calculating the 30 Hp 3 phase AC motor of power what size of cable is used for this motor?