what do you mean by 1 ton in AC`s
Answers were Sorted based on User's Feedback
The cooling produced by melting of 1 ton of ice in a day is
taken as unit of refrigeration (in tons). Now unit of
refrigeration used in S.I. System is KW.
1 ton of refrigeration
= mass of ice x latent heat of ice / 24 hrs
= 900 kg x 335 KJ/Kg ( one short ton = 900 kgs )
------------------
24 x 3600 secs
= 3.4895 KJ/Sec
say 3.5 KJ / Sec = 3.5 KW
that is 1 ton of refrigeration = 3.5 KW
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / ravi shanker
the amount of refrigeration effect produced to melt 1000kg of ice in 24 hours.
1TR=1000*335kJ in 24hours (latent heat of ice=335kJ/kg)
= 1000*335/24*60
=232.6kJ/min
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / anand g
It means " removal of heat by a system required to melt 1 ton of ice in 24 hrs.......
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / amit sonmale
First Standard For 10*10Sq Ft Area
BTU=Wght(Kg)*Sp.Heat*Temp Diff.
=800Kg*1*15
=12000British Thermal Unit
1Tr =12000Btu
| Is This Answer Correct ? | 6 Yes | 6 No |
Answer / gopal manikpuri
1 ton AC means this AC can able to extract that amount of
heat/hr through which 1 ton water of zero degree, can be
convert to ice of zero degree.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / nawaz
It means that in a closed room(at room temperature)the
cooling effect realized when u melt 1000kg of ice for 1 day.
1 ton = 12,000 BTU {Heat Removal/hour}
BTU system is followed in USA,UK & India
| Is This Answer Correct ? | 3 Yes | 4 No |
Answer / pramod
it means capacity to cool one ton of air in 24hrs.
| Is This Answer Correct ? | 5 Yes | 6 No |
Answer / ar.dinesh
The amount of the heat required to convert 1 ton
of ice in to water within 1hours. The initial
temperature of water is 0 deg C.
| Is This Answer Correct ? | 1 Yes | 2 No |
What do you mean by transformation ratio of instrument transformer?
Transfer function is == ? a. Mathematical model b. System with no physical structure c. Can be calculated through differential equations
WHERE NEUTRAL WIRE IS CONNECTED AT DOMESTIC TO TRANSMISSION LINE(SINGLE PHASE TO THREE PHASE)
design of IGBT firing circuit for 11KV
If single phase supply is 220v. then why three phase supply is 660?
why we are using the 2 slope in differential relay?but in busbar differential we are using only one slope. what is the reason.
what is meant by impedance testing of transformer and why it is used
What is best method of Calculating Short Circuit current in power system network.
What are the different types of hydro schemes?
If we have 630kva step down transformer to operation 3 phase motor 150 kva which size of cable is used? at circuit breaker to 3 phase motor or to electrical board
I have 380.KVA Volva Penta DG set. Tell me how to calculate units from KWH reading....
Is there is any difference between AC and DC Cables
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)