what do you mean by 1 ton in AC`s
Answers were Sorted based on User's Feedback
The cooling produced by melting of 1 ton of ice in a day is
taken as unit of refrigeration (in tons). Now unit of
refrigeration used in S.I. System is KW.
1 ton of refrigeration
= mass of ice x latent heat of ice / 24 hrs
= 900 kg x 335 KJ/Kg ( one short ton = 900 kgs )
------------------
24 x 3600 secs
= 3.4895 KJ/Sec
say 3.5 KJ / Sec = 3.5 KW
that is 1 ton of refrigeration = 3.5 KW
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / ravi shanker
the amount of refrigeration effect produced to melt 1000kg of ice in 24 hours.
1TR=1000*335kJ in 24hours (latent heat of ice=335kJ/kg)
= 1000*335/24*60
=232.6kJ/min
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / anand g
It means " removal of heat by a system required to melt 1 ton of ice in 24 hrs.......
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / amit sonmale
First Standard For 10*10Sq Ft Area
BTU=Wght(Kg)*Sp.Heat*Temp Diff.
=800Kg*1*15
=12000British Thermal Unit
1Tr =12000Btu
Is This Answer Correct ? | 6 Yes | 6 No |
Answer / gopal manikpuri
1 ton AC means this AC can able to extract that amount of
heat/hr through which 1 ton water of zero degree, can be
convert to ice of zero degree.
Is This Answer Correct ? | 1 Yes | 1 No |
Answer / nawaz
It means that in a closed room(at room temperature)the
cooling effect realized when u melt 1000kg of ice for 1 day.
1 ton = 12,000 BTU {Heat Removal/hour}
BTU system is followed in USA,UK & India
Is This Answer Correct ? | 3 Yes | 4 No |
Answer / pramod
it means capacity to cool one ton of air in 24hrs.
Is This Answer Correct ? | 5 Yes | 6 No |
Answer / ar.dinesh
The amount of the heat required to convert 1 ton
of ice in to water within 1hours. The initial
temperature of water is 0 deg C.
Is This Answer Correct ? | 1 Yes | 2 No |
what is meaning of bus raiser???
why full load voltage is less than no load voltage?
whenever any squirrel or a crow falls on the transformer input line then there is a big explosion and 440 volts of power is being discharged through the neutral line due to which appliances in off mode are also burned.we have earthing for the transformer as well as the bus bar chamber.why is it happening?
For R-L or R-C ckt,time constant formula is L/R and RC respectively and its unit is in sec.Pls tell me the derivation
What is the real function of reverse power relay in generator panel while syncronising?
how solar power plant energy meter multiplication factor
what is the difference between 5P20 class CT , PS Class CT and 5P10 class CT??
What is systematic error?
When should I use earth leakage circuit breaker for incomer and when should I use it for each feeder seperately?
what is the reason for balance of voltage in magnetic balance test?
transmisssion type
tell me about xlpe cable?