why we are using the 2 slope in differential relay?but in
busbar differential we are using only one slope.
what is the reason.
-on lowZ differential, when fault happens, CTs going to go saturated. slope aims to compensate error due to CT saturation because CTs have different characteristic.
-for busbar protection, it is HiZ differential, one slope because all CTs have same charracteristic. no need to compensate
| Is This Answer Correct ? | 0 Yes | 0 No |
Can we use both Electrical & mechanical interlock between tow breakers? if yes how, please explain
What is the difference between line Distance protection and Line Earth Fault Protection?
What is the formula for finding fault level of generator?
What is different between Circuit breaker and Isolater?
why we use low kv lightining arrester in line for example 9 kv using in 11kv
How CT is connected to measure current by changing plug setting , ratio is 300 - 150 / 5 A ?
1 Answers Ajanta Pharma, Bhel, Cosmo Films, Suzlon,
What is difference between ON delay and OFF Delay Timer?
There are Two questions about Steam Turbine Generator... What is HRSG bypass of LP, HP used for in power generation? In particualar, in the event that fault of HP bypass, there would be STG TRIP in operation but none on the LP bypass fault...what's the reason ?
WHERE to use CVT & PT.
what is the safty of poly phase tranformer?
can we use ACB for HT supply
a motor's measured current is 45amp,whereas the rated current is 38 amps but still it is running ,how?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)