why we are using the 2 slope in differential relay?but in
busbar differential we are using only one slope.
what is the reason.
-on lowZ differential, when fault happens, CTs going to go saturated. slope aims to compensate error due to CT saturation because CTs have different characteristic.
-for busbar protection, it is HiZ differential, one slope because all CTs have same charracteristic. no need to compensate
Is This Answer Correct ? | 0 Yes | 0 No |
control diagram of star delta starter
Why can't we parallel the secondary circuits of two voltage transformers?
Consider a case that two 200 hp motors are connected to 500KVA transformer. For improving power factor can we add capacitors in common bus bars to motors. Or should we add capacitors for each individual motor?
why dc is used in control circuit for mv & hv switchgear instead of ac
How can we calculate ngr resistance for a generator and Transformer ? What type of transformer requires ngr ?
How harmonic block test are conducted on relays ( Siemens,Areva ect )power transformer using omicron kit?
In case of HV test on medium voltage cables, BS is asking for 4 U0 where as IEC is asking for 3.5 U0. Can any one advise me how this 3.5 times or 4 times U0 is derived?
What is power factor? Whether it should be high or low ? why?
Star Delta Diagram with full description
0 Answers SKS Microfinance, Syscom,
i am using auto transformer for starting of induction motor to provide reduse voltages...but the principle of a tansformer according to definition"which transform energy to on circuit to another circuit with constant power and constant frequency". so if i am using reduse voltage then current obsely hige because power is same.but we use auto transfarmer for starting of induction motor to give low current.but here according to definition we are giving hige current.
What is meant by reset level of the relay?
True or false question. 1.The fuse provide phase and neutral 2.power loss in electrical circuit can take place in (resistance or inductance or capacitance). 3.two phase system each phase has separated by a phase difference of (90 or 180 or 270 or 45). 4.3 phase balanced star connected load neutral current shall be (line current or phase current or zero or unity)