Answer / nur.asidik

-on lowZ differential, when fault happens, CTs going to go saturated. slope aims to compensate error due  to CT saturation because CTs have different characteristic.
-for busbar protection, it is HiZ differential, one slope because all CTs have same charracteristic. no need to compensate 

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

control diagram of star delta starter

5 Answers  


Why can't we parallel the secondary circuits of two voltage transformers?

0 Answers  


Consider a case that two 200 hp motors are connected to 500KVA transformer. For improving power factor can we add capacitors in common bus bars to motors. Or should we add capacitors for each individual motor?

2 Answers  


why dc is used in control circuit for mv & hv switchgear instead of ac

0 Answers  


How can we calculate ngr resistance for a generator and Transformer ? What type of transformer requires ngr ?

5 Answers   Welspun,






How harmonic block test are conducted on relays ( Siemens,Areva ect )power transformer using omicron kit?

0 Answers   Siemens,


In case of HV test on medium voltage cables, BS is asking for 4 U0 where as IEC is asking for 3.5 U0. Can any one advise me how this 3.5 times or 4 times U0 is derived?

0 Answers  


What is power factor? Whether it should be high or low ? why?

9 Answers  


Star Delta Diagram with full description

0 Answers   SKS Microfinance, Syscom,


i am using auto transformer for starting of induction motor to provide reduse voltages...but the principle of a tansformer according to definition"which transform energy to on circuit to another circuit with constant power and constant frequency". so if i am using reduse voltage then current obsely hige because power is same.but we use auto transfarmer for starting of induction motor to give low current.but here according to definition we are giving hige current.

0 Answers  


What is meant by reset level of the relay?

0 Answers  


True or false question. 1.The fuse provide phase and neutral 2.power loss in electrical circuit can take place in (resistance or inductance or capacitance). 3.two phase system each phase has separated by a phase difference of (90 or 180 or 270 or 45). 4.3 phase balanced star connected load neutral current shall be (line current or phase current or zero or unity)

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)