Answer / sewagudde
Reason you dont get a shock is that the earth loop path
provides a much lower resistance than the body and
electricity always chooses the path of least resistance.
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / debasis
Q. 1> Without a close loop ckt., no current flow.
It should be a close loop path.
Example: If earth fault occured in your home, then current
flowing through earth to transformer neutral(star) point as
the star point of a transformer is grounded.
Q. 2> If you touch the above faulty appliance, idealy,
there should be no effect. But practically, A small current
will flow through body because ur body resistance is in the
range of few kilo to mega ohm. But nothing to be serious.
Thats why we provide earthing.
| Is This Answer Correct ? | 2 Yes | 1 No |
Can a generator runs after getting 1st stator earth fault.
What is the difference between resistance grounding system and resistance earthing system?
What will happen if we on 200kvr capacitor bank(11kv in bus)If there is low load on transformer (1.5 mva 33/11 kv)
What is Long rod insulator and it's applications..? merits over the disc insulator ..?
What is Transformer?
What is a current transformer?
Why the arms of delta in a delta-wye power transmission system are kept constant??
how to calculate the size of the HT cable
if 2500 KVA TRANSFORMER CAPACITY.33KV INCOMING HOW ARE AMPEAR PRIMERY SAID
11kv/0.433kv, 2 mva , transformer , for protection and metering how many CT/PT are required?
what is cause of static electricity? I experience shock when i touch metal equipment in a room ,furher check shows earth leakage showing 80ma at the DB near to the 400 MCCB?
how to calculate the surge level of surge suppressors related to the SF6 cicuit breakers?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)