Electrical Diagram of Electric Arc Furance from transformer
to Furances
The cuurrent in the secondary of the arc furnace will be
very high i.e. in kA. Hence the secondary will be devided
into no. of small bus bars and will be connected to the 3
electrodes to form a Delta, using copper hollow tubes and
flexible hoses. Water will be circulating in the copper
tubes for providing cooling. There will be a provision to
change the primary connection either in star or in delta.
Three single phase transformers can also be used instead of
only one 3 phase transformer.
Is This Answer Correct ? | 3 Yes | 0 No |
what is the IS foe lightning arrester?
a induction motar has 30-35% exciting current at no load but in transformer it is only 2-3% ofbrated current why any reason?
What is the difference between Zero Current Transformer and Core Balance CT ?
when u are given a timer,push buttons and contactor, how do i practically make a star delta control circuit and a direct online control circuit?
What are the Safety Steps While Inspection the LT Panel.
how do you reduce the skin effect
what is the use of terminals in transformer ?
1 Answers Core Solutions, Honeywell,
why select the 3 phase power supply system in electrical system.
What is the procedure/activities to be taken to inject the current more than 2000A by using 2000A Loading Transformer?
how can we measure the import power and export power in the same line?
exact difference between electronicsand electrical
on 22.03.2015 at 17:15hrs Y phase 66kV class Power Trf-2 Current transformer has flashed over and oil came out. The failed CT has been replaced on 24.03.2015 at 13:15hrs and the Trf has been charged in presence of RT Hassan after conducting the pre-commissioning tests. On the same day at 17:00hrs the commissioned CT has again flashed over and immediately the Trf has been isolated from power supply. It is confirmed the secondary is not opened and checked the earth integrity and is found ok. Here what would be the reason for the CT failure?