Synchrounous motor is three phase motor,but its not self
starting .why?
Answers were Sorted based on User's Feedback
Answer / prasanth
"A synchronous motor is not a self starting motor because
torque is developed when running at synchronous
speed,therefore,the motor needs some type of device to
bring the rotor to synchronous speed."
EXPLAINATION:
As per operating principle of synchronous
motor,due to continuous and rapid rotation of stator
poles,the rotor is subjected to a torque which tends to
move it first in one direction and then in the opposite
direction.Owing to its large inertia,the rotor cannot
instantaneously respond to such quickly reversing
torque,with the result that it remains stationary or in
other words it is not self starting.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / koti1965
Seen 20 answers, none of them are correct. since the rotor is not closed, no induced current and hence no torque(the basic principle of rotation ac motor). So give supply to rotor(runs as SM) or short it(runs as IM).
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / lloyd kaunde
Its simply because each rotor pole of the motor is subjected
to both attraction and repulsion forces
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / soumya sephalika roul
Synchronous motor is not self-starting because RMF rotates at NS speed and rotor is stationary.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / leo thomas
Since the rotor is supplied from a DC source the rotor have
a permanent polarity . But applying 3 phase supply to
stator, a 3 phase magnetic field is produced , but polarity
changing according to the supply frequency . Actually at
some regular time intrvals the stator poles and rotor poles
comes into exat 120 degree phase shift (this will exist
only for some micro seconds)the motor try to rotate a
clockwise direction . Another time intervels motor getting
torque to counter clockwise direction .
Thus the rotor poles oscillating to clockwise and
anticlockwise direction, due to the inertia of the moving
system it cannot move into any direction
| Is This Answer Correct ? | 2 Yes | 3 No |
Answer / vikash kumar gaurav
similar pole are alike each other it is a three phase motor
bt very low starting torque and the average exerted torque
in operation of synchronous motor is zero and we have to
supply both the rotor and stator this is another cause it
is nt aself starting machine.
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / tulsi_lotus@yahoo.com
sync motor has no self starting torque this is bcaz its
high inertia prevents it from rotating in either of the
direction,so it is not self starting
| Is This Answer Correct ? | 4 Yes | 10 No |
Answer / rahul
becoz in synchronous machine uni-directional torque not
produce.
| Is This Answer Correct ? | 3 Yes | 9 No |
Answer / vidhya
because of the rotor inertia it is unable to rotate in the
anticlockwise direction as the energy supplied is
insufficient to make it to spin because it is very
heavy....so a prime mover is required to produce a
unidirectional torque.
| Is This Answer Correct ? | 4 Yes | 11 No |
Answer / sangeetha
Synchronous motor is not self starting. Because to develop
torque motor has to run at synchronous speed. the motor
needs some type of device to bring rotor to synchronous
speed.
| Is This Answer Correct ? | 5 Yes | 14 No |
for 11KV OH system what will be typical per KM "R" "L" "C" parameter. for 33KV OH system what will be typical per KM "R" "L" "C" parameter. for 33KV UG system what will be typical per KM "R" "L" "C" parameter.
what is inverter
WHAT IS THE MEANING CREEPAGE DISTANCE
Operation carried out in thermal power stations?
What is difference between Harmonic and Non harmonic Capacitor Bank?
hi can you give any body fault level calculation, generator fault level calculation,transformer fault level calculation for system fault level with equation? i have 3.3kv generation voltage three gas gen sets, one is 1.9MW,2nd is 2.5MW,& 3rd is 3.8MW & i have 11 kv generation voltage one gas gen sets is 3.8MW, we are step up to 22kv by transformer
3 Answers Hindalco, Piramal Healthcare,
1.what is difference in maintain Hz again Hz in USA ? 2.how to calculate the battery AH? 3.why are yearly maintained in transformer how many tests in required?
what is meant by unity power factor?unity means one why dont call 2,3,4......?
Advantages of using generator circuit breaker (GCB) scheme in a power station ?
100V supply is appllied between 500K Resistance bulb. for 1 kwh energy, how long time the bulb will glow? explain the calculating method.
What are methods to avoid the inrush current at the time of starting of power transformer ?
How to increase the specific gravity of DG batteries?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)