in 11kv/400v transformer when only one phase of 11kv supply
fails what happens to sec voltage and why
Answers were Sorted based on User's Feedback
Answer / sunit
from my point of view what i have seen physically .. if one phase of the 11kv line is faulty or jumper in transmission lines burnt out then there will be a low voltage in the secondary side of transformer,
actually DTR breaker in control room needs to trip the circuit but if the relay time settings are not accurate then it won't trip the circuit rather show low voltage in the secondary side...
| Is This Answer Correct ? | 2 Yes | 0 No |
If delta/star ,one phase voltage will be normal and the
other two 50%, If star/star two phases normal and the third
missing
| Is This Answer Correct ? | 5 Yes | 4 No |
Answer / b.janardhana rao
I seen physically. One phase of 3 phases failure in HT. I said Example it will shows like RY - 415, YB-415, BR - 230Volts in seconary side. In that time two phases what loads are there is working. Remaining phase is not working. So 3 phase loads like pums, motors are not working. So we can put in ACB phase failure relay to be used. In that case the ACB breaker wads tripped.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / suresh
HT side one phase fails means secondary side unbalance voltages coming ,that means upstream side breaker will trip within time limit.
| Is This Answer Correct ? | 0 Yes | 2 No |
11kv/415v T/F is designed for 3 phese supply , if 1 phase
fails then t/f will trip automaticly and no voltage will be
avaliavle at secondary side.
| Is This Answer Correct ? | 11 Yes | 17 No |
Answer / m.prasath
Here,
Primary voltage is 11kv.
Secondary voltage is 400v.
If primary voltage is failed means nothing will happen in secondary side. ie almost zero in secondary side in transformer....
| Is This Answer Correct ? | 6 Yes | 12 No |
What will be the voltage regulation of a full load and 0.80 power factor lagging load transformer when a two winding single phase transformer has a voltage regulation of 4.5% at full load and unity power factor?
Consider three heater bank connected in 3 phase star with neutral.Each heater bank connected in each phase.So each phase get 230 volts supply.my question is,during balance condition, current flow in neutral or Not
In winding design, the angle of chording (β) is nearly equal to A 45 degree B 60 degree C 30 degree D 90 degree
what is the power factor of an inductive load ? (i) Zero (ii) Lagging (iii) Leading (iv) Unity
what is meant by crawling??
Why the electron flow in reverse of current.
sir please send me previous year questions of jspl through which i could prepare myself fpr the test.
64 Answers FGH, HFT, Jindal, Jindal Steel and Power, JSP, JSW, Lin Engineering,
What is meant by RVT and NDR ? expansion and details of it
What kind of battries are generaly used with Disel Generator?
Is there any difference in AC current/ DC current carrying capacity of a conductor .What can be maximum current handling capacity of a 2.5mm stranded cu cable when connected to AC and DC supply.
explain why the armature voltage changes when the field rheostat is varied in self excited DC generator
how to calculate cable size by amp
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)