Answer / sunit
from my point of view what i have seen physically .. if one phase of the 11kv line is faulty or jumper in transmission lines burnt out then there will be a low voltage in the secondary side of transformer,
actually DTR breaker in control room needs to trip the circuit but if the relay time settings are not accurate then it won't trip the circuit rather show low voltage in the secondary side...
| Is This Answer Correct ? | 2 Yes | 0 No |
If delta/star ,one phase voltage will be normal and the
other two 50%, If star/star two phases normal and the third
missing
| Is This Answer Correct ? | 5 Yes | 4 No |
Answer / b.janardhana rao
I seen physically. One phase of 3 phases failure in HT. I said Example it will shows like RY - 415, YB-415, BR - 230Volts in seconary side. In that time two phases what loads are there is working. Remaining phase is not working. So 3 phase loads like pums, motors are not working. So we can put in ACB phase failure relay to be used. In that case the ACB breaker wads tripped.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / suresh
HT side one phase fails means secondary side unbalance voltages coming ,that means upstream side breaker will trip within time limit.
| Is This Answer Correct ? | 0 Yes | 2 No |
11kv/415v T/F is designed for 3 phese supply , if 1 phase
fails then t/f will trip automaticly and no voltage will be
avaliavle at secondary side.
| Is This Answer Correct ? | 11 Yes | 17 No |
Answer / m.prasath
Here,
Primary voltage is 11kv.
Secondary voltage is 400v.
If primary voltage is failed means nothing will happen in secondary side. ie almost zero in secondary side in transformer....
| Is This Answer Correct ? | 6 Yes | 12 No |
In a Tap changing transformer where is the tap connected , is it connected in the primary side or it is connected in secondary side
What is the maximum allowed kwa through 2.5mm cable. Electric company installed 2 electric meter at my premises . Two jumper wires of 2.5 mm are used to connect . 2 single phase meters with allowable load 6 and 3 kwa. These jumper wires are taken from a 3 phase electric meter. Meters are in open Sun. What max load these wires can take.
the inertia constants of two machines are respectively 30and 42 MJ per MVA.when the change in frequency due to change in load in first machine is 12 Hz,the change in second machine frequency will be?
WHAT IS ELECTRICAL MAINTAINTENCE ?
draw the block diagram of fire alarm?
What is Procedure the procedure to select CT's & PT's in 66kV and above substation?
why u want to work in sail/ntpc as u r already in an it company where life is good, good environment no much tensions etc?
Is there any local or International standards that prohibit the installation of earthing pit in the planters area where the earthing pit is subject to continues soak in water?
voltmeter kya hota hy ?
What is the size of a 60 watt and 80 watt tubelight?
Why a transformer is known as a static device?
explain Uninterrupted power supply detailed electronical operation with circuit diagram
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)