Do you know the faults occurs generally in motors and how
to rectify them?
Answers were Sorted based on User's Feedback
Answer / shailza
general occuring faults in motor are:
1. inst. overcurrent
I(1)the current is equal to 8.5 times the nominal current
rectification-isolate breaker, take megger and check motor
T.B
2. Earth Fault I(0)
rectification-take megger
3. Stalling I1(t)
rectification- take no load trial with decoupling of motor
4. Thermal overload Ith
rectification- check current balance
5.phase imbalance I(2) Check motor T.B and take megger.
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / kannan
1. Over load tripping - Reset OL relay.
2. Ball bearing failure - To be identify by heavy noice and
offton tripping & Over heat - Change bearing.
3.Monthly once clean the body of the motor. cooling will be
better.
4. Winding problem. - Check by megger of multi meter.
Rewinding to be done.
5. Over load relay itself problem some times.
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / pabs
Winding gets damage
If any Brake pad in motor also get damaged
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / kokkiligadda venkata raju
over load trip
to control the ratings
under maintenance problem that means lubrications,cleaning
in this minimise to proper maintenance
remove the light damage parts in this cause to totally
motor damazed
it' minimise to replace the parts
over temperature
it's minimise to fix the fans to rotor
| Is This Answer Correct ? | 0 Yes | 0 No |
what is zinc diffusion?
what is derating factor in Cable ? how we minimise this?
18 Answers Bhel, College School Exams Tests,
Why in USA supply voltage parameters(230V,60Hz)are different,is there any advantage please brief.
Suppose i Have an Ac motor of 25Hp 1500 Rpm 50 Hz Can i run a motor 2500 Rpm by AC drives by increasing a frequency either it safe or not ....
why fan consume constant power even when we increase or decrease its circuit resistance through speed regulator???
why transformer ratings in kva? & DG ratings in kva? & Motor ratings in kw/HP?
In Slip ring Induction Motor we use Liquid Rotor Starter for Starter Every Time Liquid Filling we need add Soda Sodium Carbonate or only Distilled water is Enough.
what is difference between AC VVVF drive & Dc VVVF drive explain their working principle?
what is use of thermistor ?
HOW TO CALCULATE THE DOMESTIC POWER FACTOR?
What are the conditions to be satisfied before connecting two DC generators in parallel?
Why A.C. capacity given in Ton. Ex. - 1.5 Ton
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)