what is the difference between OSR and BUCHHOLZ relay of transformer?
Answer / sanskar
Difference between Buchholz Relay and Oil Surge Realy:
Generally there is confusion between operation of Buchholz relay and Oil surge relay.
So, Let me interpret the major differences between them.
Buchholz Relay
Oil Surge Realy
Buchholz relay is used for protection of oil filled transformers/reactors fitted with conservators against low oil level and internal faults.
OSR is used to report any malfunction developed inside the On Load Tap Changer Chamber.
Buchholz relay is Gas actuated Relay.
OSR is Oil actuated Relay.
Buchholz relay should be mounted in the connecting pipe between the transformer and conservator tank.
OSR is installed in the pipe between OLTC head and the oil conservator.
Buchholz relay is actuated by the gases flowing through and accumulated in relay.
OSR relay is actuated when the flow rate of oil exceeds the preset value.
Buchholz relay detects the fall in oil level due to formation of gases after any internal fault inside the transformer.
OSR detects excessive oil surge after any fault occurs inside OLTC Chamber.
| Is This Answer Correct ? | 4 Yes | 1 No |
how we select the mva rating of the circuit breakers?
why the earth terminal in three pin top is longer than rest of the two terminal and of bigger size?
HOW CIRCUIT BREAKER RATING CALCULATED?WHAT ARE THE PARAMETERS CONSIDERED?
why grid failure happens?
Could the power factor on electrical system can affect the registration of the kwhr meter or the CT/PT?
either water sensor or flow meter,how we observe the water level, f any other equipment are in market ?
HOW EFFICIENTLY LOAD IS SHARED BETWEEN ALTERNATORS
what is V.L.F. testing of power cable? do you know the voltage ratings, like for what rating and size of cable what rating of V.L.F. testing is used?
why circuit breaker closing time is always higher then tripping / opening time.
State the points to be considered for selecting a particular type wiring.
i am an maintenance engineer. one distribution board have 5 feeder. recently its ELR trips frequently, but it take some times after trip( 10min,20min..)but 3 feeder no load. two feeder only loaded. i checked one feeder IR value all values are above 50Mohm.but B phase to Earth is only 9Mohm.any problem about low value
A LT ckt i mean 440 volt flow of current100A.at this time HT current what will ON 11 KV &33 KV.plz givemy answer with example
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)