why ac generator ratings in kva only why not kw ?????????????
?
Answers were Sorted based on User's Feedback
Answer / mahavir jagdev
Because you don't know what power factor the generator will be loaded with. The KVA denotes the Voltage and the Current the generator can take at resistive load.
| Is This Answer Correct ? | 10 Yes | 4 No |
Answer / raul
the designs and ratings of electric machines such as
alternators, transformers etc are always decided by the
amount of losses taking place in d machines i.e. core loss
and copper loss. since the core loss depends upon the
applied voltage and copper loss depends upon d load
current, therefore the product of these dependent variables
i.e. voltage and current i.e. KVA is the acutal ratings.
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / at
Not only generator but UPS / Transformer or any other
device which is giving Electrical power as output is rated
in kVA. The reason is that it is power that will be given
by the machine apperently. however when the load is
connected say for example a motor the actual power which is
converted to work is diffenrent known as active power and
involves power factor. There fore all machines with
mechnical output are rated in kw.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / s a s i
rating means max capability of sym.it will obtain from
nether voltage nor curent with resistance known facor.but
kw not provides voltage r current.it gives only wattage
only.so it will rated in kva..
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / amit kumar
due to two losses iron loss and copper loss.iron losss
measured in volt where as copper loss is measured in
current.
| Is This Answer Correct ? | 4 Yes | 4 No |
Answer / sunil
ac generator or any ac machine have two powers real and
reactive power. va or kva is the apparent power of the
machine which is near to the real power and best describes
the capacity.
| Is This Answer Correct ? | 3 Yes | 5 No |
Answer / murari.soma sekhar
THE RATING OF ANY MACHINE IS DEPEND ON LOSSES DISUPATION OF
THAT MACHINE.SO IN CASE INCASE OF ELECTRICAL MACHINE THE
LOSEES ARE COPPER LOSES @IRON LOSSES BOTH RESULT IN
DISUPATION OF HEAT .HENCE THE CU LOSS DEPEND ON CURRENT
@IRON LOSS DEPEND ON VOLTAGE.SO THAT PRODUCT GIVES RATING
OF MACHINE.
| Is This Answer Correct ? | 0 Yes | 3 No |
what is the use of Auto re-closer?
we have provided 30 nos. relay contacts in panel.I want to know how do we do the numbering for the relay contacts as per any applicable standards
what is wore of PLC ?
what is the use of pmg in exciter?
why the all high voltage transformers are in 11kv , 33kv , 66kv, 132kv like that
why the current leads voltage in the case of a capasitor
Differentiate between Zero and Negative sequence current
What is reason of rating of transmission line multi pal of 11 like as 11/33/66/220 ? Why not use 75 kv 23 kv line in power system ?
1 Answers Apollo, Balco, Bhel, Vardhman,
What is the constructional difference between ceiling fan and table fan
in 33/11kv stepdown transfomer, transformer will stepdown to 11kv & remaining 22kv where it will go..
plzzzzzzzzz plzz send me the papers of JSPL WRITTEN TEST..SO that i can prepare for the test in electrical engg..
Why Stabilising Resistor used in REF circuit ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)