3 phase supply is there Total kw 100 howmuch cable put the load
Answers were Sorted based on User's Feedback
Answer / khaled shaban
you have to calculate your ampere by using below equ.
I=P/Sqrt(3)*V*P.F
after that you have to select circuit breaker; after selection of CB check cable size referring to cable ratings as per manufacturer.
e.g. Volt 380V, with 100Kw and consider P.F=0.8
current will be 190A
cable should handle more than 190A, but first you have to choose MCCB for this load; the standard for your selection should be as following:
MCCB size = I*1.25 (1.25 at least)
so MCCB will be more than 237.5A (for standard MCCB you will select 250A)
hence your MCCB is 250A, your cable should be more than 250A.
As per cable manufacturer rating in my country, cable size should be (3*120+70)mm2 laid in duct, but in case if this cable laid in ground; cable size will be (3*90+50)mm2.
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / g ravikanth
3core xlpe 95 sqmm or 3 x 120sqmm single core cable can be used.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / jithendra
For 100 KW for 150amp's load
125 SQmm copper cable or 185 SQmm Alummium cable
Is This Answer Correct ? | 1 Yes | 0 No |
to vary valtage from 0 - max a variac is necessary . so how to design for high power applications nearly about 200KW power
how to set the transformer differential relay
What is the type of electrical motor used in mining industries?
for star delta connection,,why the contactor star not burn,when red,yellow and blue cable is looping.
2 Answers Mahindra Water Utilities,
What is meant by analogous system?
what is the difference between ac ground and dc ground.. In my project iam using both ac and dc supply.. can both the grounds or the return paths be connected??
what is ALF and ISF in current transformer?
on a three-winding transformer relationship delta-delta-star, on third winding why the relationship is a star? what are the advantages and disadvantages? Thank you and please help
what is the frequency standard with tolerance level for India?
why single phase induction motors are not self staring ? how can we start the 1-phase Induction motor ?
A parallel flow heat exchanger will perform better than a counter flow heat exchanger. State if the statement is true or false.
1.what is the basic difference between surge arrestor and lightning arrestor and where we use it. 1.what is the difference between metal oxide without gapped lightning arrestor and with gapped lightning arrestor